The report is: Sprinkler Protected Car Stacker Fire Test Prepared for: The British Automatic Fire Sprinkler Assoc. 11 Dec 2009 Client Report No. 256618
Conducted by breglobal It is applicable to THEIR standard stack arrangement where the cars are stored differently above/below each other at an angle. There must be 4 sprinklers, one at each corner of the car with an overall OHG2. It controlled the fire and temperature but did not extinguish it. Its a good starting point. Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org On Aug 13, 2013, at 1:31 PM, Roland Huggins <[email protected]> wrote: > This issue was addressed by fire testing on the other side of the pond (aka > UK). I dig around and look for the report which I need anyways for the > upcoming NFPA 13 Forst Draft meeting. There is a Public Input on just this > topic. If memory serves me right (not a consistent tool), it is less of a > problem than most of us think. > > Roland _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org