Ron I missed the part in Bobs post about the butterfly valves. When we have done this we used a Wilkins 350ADA with a Post Indicator valve, which is on the approved list, the water guys over here are trained by the water guys over there so they are no easier to deal with. I did not see that Bob was proposing a PI valve in addition to the Backflow preventer.
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Ron Greenman Sent: Wednesday, August 21, 2013 1:45 PM To: [email protected] Subject: Re: WPIV Bill, I'm surprised your water guys are letting you do this. Happy about it, but surprised. This side of the hills that wouldn't happen as the "listing" would void if you change the valve type/style that comes with the assembly. I even asked USC about this as the only difference between OS&Y, NRS, & PIV is the operating mechanism. They said no. Maybe something has changed. Sent from my iPhone On Aug 21, 2013, at 12:17 PM, "Bill Cunningham" <[email protected]> wrote: > Bob > We always put them on the #2 shutoff valve, due to the fact that when the > backflow valve is being tested annually the #2 shut off valve is shut off > for the test and the #1 valve is open and closed numerous times during the > course of the test. If it is in a vault the tester has to crawl in and out > of the vault numerous times to open and close the #1 shutoff valve to > perform the test. Would be easier on a wall PIV in that they would only have > to walk in and out of the building numerous times. Depends if you like the > local backflow tester. We have several testers on staff so we try to make > their life a little easier. > Bill Cunningham CET > Plumbco Inc > > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Bob > Sent: Wednesday, August 21, 2013 11:54 AM > To: [email protected] > Subject: RE: WPIV > > thanks > > Bob Knight, CET III > 208-318-3057 > www.firebyknight.com > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Forest > Wilson > Sent: Wednesday, August 21, 2013 12:45 PM > To: [email protected] > Subject: Re: WPIV > > That can depend on the AHJ. > For example in Ohio the water purveyor has jurisdiction up to and including > the backflow. > Building Dept has jurisdiction after backflow. > > I would send an RFI to the Architect or send an email to the Water Dept or > building official and ask if they care. > > Sent from my iPhone > > On Aug 21, 2013, at 2:02 PM, "Bob" <[email protected]> wrote: > >> I have a situation where a backflow w/ bfly valves is being used. A >> WPIV is also required. In this situation is the proper place for the >> WPIV before or after the BFP? I would think before, just from a >> maintenance standpoint, but I have learned over the years that what I > think isn't necessarily right. >> >> Thanks, >> >> Bob Knight, CET III >> 208-318-3057 >> www.firebyknight.com >> >> >> >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl >> er.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > ----- > No virus found in this message. > Checked by AVG - www.avg.com > Version: 2013.0.3392 / Virus Database: 3211/6596 - Release Date: 08/21/13 > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org