Actually this is not a 13 question but a 14 question.  As such, you have to 
resolve 14:6.1.2.2 that requires mains etc to be protected with fire rated 
construction equivalent to that of the stairwells.  Then 6.1.2.2.1 allows the 
mains in sprinklered buildings to be unprotected.  So going through an 
unprotected portion of the building kicks you back to protected with rated 
construction.  There have been equivalencies granted whereby the main is 
protected with a row of sprinklers (typically installed on the main itself).  
Thats a call by the AHJ.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Aug 30, 2013, at 9:34 AM, "James D. Waite" <[email protected]> wrote:

> We have a phased project, and I have to run a standpipe feed through an 
> unsprinklered area.  Is there any more guidance than NFPA 13 ('10 Ed.): 
> 8.16.4.3.2?  I'm planning on providing a single line of sprinklers near the 
> feed pipe.  Is there a requirement on how close those heads need to be?
> 
> Jimmy Waite, CET - Design Manager
> Fire & Life Safety America- Raleigh District
> 7711 Welborn Street, Suite 103
> Raleigh, NC  27615
> Office: 919-872-3250
> Cell: 919-868-3546
> Fax: 919-877-5775
> www.flsamerica.com
> 