> Scenario - a 2 story building
>
> There is a vertical tire carousel that goes through a mezzanine – hole
> sized at 6’-4 x approx. 17’ which sits in the corner of the storage area
> (general car parts) – to the 2nd floor. – The entire height of the
> carousel is 18-7” from the ground level.
>
> If we were to place a row of sprinklers along the wall (nothing above
> them  all the way to the 2nd floor ceiling) and then on the opposite side
> under the mezzanine, could we in effect comply with NFPA #13 2007 ed -
> Table 18.4(a) (6) - for one row of in rack sprinklers so we could calculate
> the system on the 2nd floor at .40 gpm?
>
> This is a strange deal to me because it would seem like overkill to have a
> .90 density to protect such a small area and then increase it by 15’-0 on
> the 2 sides as required.
>
> Thanks for your help
>
>
> --
> Greg McGahan