Greg,

I haven't run into this situation before, but I've done a few tire stores. A 
possibility would be to design the sprinklers for the tire storage on each 
level and put a water curtain around the opening. Also an interlock to shut 
down the carousel. You might have to increase the density over the opening as 
well as you noted. Challenging situation. Look at requirements for protecting 
conveyors to see if that gives you insight. 

Disclaimer: This is a guess based on limited knowledge. Take it as such.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com

On Sep 4, 2013, at 8:29 AM, Greg McGahan <[email protected]> wrote:

> No takers? Anybody home?
> 
> 
> On Tue, Sep 3, 2013 at 6:06 PM, Greg McGahan <[email protected]> wrote:
> 
>> Scenario - a 2 story building
>> 
>> There is a vertical tire carousel that goes through a mezzanine – hole
>> sized at 6’-4 x approx. 17’ which sits in the corner of the storage area
>> (general car parts) – to the 2nd floor. – The entire height of the
>> carousel is 18-7” from the ground level.
>> 
>> If we were to place a row of sprinklers along the wall (nothing above
>> them  all the way to the 2nd floor ceiling) and then on the opposite side
>> under the mezzanine, could we in effect comply with NFPA #13 2007 ed -
>> Table 18.4(a) (6) - for one row of in rack sprinklers so we could calculate
>> the system on the 2nd floor at .40 gpm?
>> 
>> This is a strange deal to me because it would seem like overkill to have a
>> .90 density to protect such a small area and then increase it by 15’-0 on
>> the 2 sides as required.
>> 
>> Thanks for your help
>> 
>> 
>> --
>> Greg McGahan
>> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
>> 1160 McKenzie Road
>> Cantonment, FL 32533
>> 850-937-1850
>> fax 850-937-1852
> 
> 
> 
> -- 
> Greg McGahan
> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> fax 850-937-1852
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to