Just received my "Sprinkler Quarterly" Magazine that addressed this specific 
issue - can't say where exactly NFPA-13 says, but NFSA addressed this issue by 
stating: Replace sprinkler if it has been removed from fitting (RC, tee, el, 
etc.). If drop nipple is removed and sprinkler stays in fitting, the sprinkler 
does not require replacement with new head.



Regards to all-



Jerry


[email protected]


Jerry D. Watts, SFPE
President & Co-Founder
ACCENT FIRE ENGINEERING INT'L. Ltd.
Santa Fe, New Mexico USA
(800) 503.1961  nationwide










-----Original Message-----
From: Todd - Work <[email protected]>
To: sprinklerforum <[email protected]>
Sent: Thu, Sep 5, 2013 6:48 am
Subject: removing sprinkler on drop


I am working on a project where we have to add heads above an existing ceiling 
on an existing system. The pendant heads are fed on swing joints. My plan is to 
have them removes the drops (with sprinkler in them) replace the 1" elbow with 
a 
tee and re-install the drops. The question came up about replacing the pendant 
heads. They were not removed from the pipe but the pipe with head was removed 
from the system. I never thought about this before and can see arguments on 
both 
sides. Replace the pendants or not?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to