Anytime a sprinkler is moved, it is potentially susceptible to damage, even if the line with an upright is backed out and left in the hanger. Or when a head in a flexible drop is moved from one location to the other. Do you require a new sprinkler every time a sprinkler is moved? Moved by how much? I think this comes down to practicality and risk tolerance.
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT www.fpdc.com On Sep 5, 2013, at 10:50 AM, "Cahill, Christopher" <[email protected]> wrote: > Except for the part 'Only new sprinklers shall be installed' which has been > around for a long time. Many would argue you have never been allowed to > reinstall sprinklers. Yes, I know there is a lot of don't ask don't tell out > there. Current edition provides clarification of the phrase only new > sprinklers shall be installed. I don't see it as a change. The > interpretation that if you pull the drop and never touch the sprinkler I'd > even argue is a little sketchy. The point of the new section is damage can > occur when you mess with the head. If you lay the drop with a head on a > table or throw (carefully) in a bucket in my mind you have risked damage. If > asked I'd say even in that case you need a new head per the code. > > Chris Cahill, PE* > Senior Fire Protection Engineer > Burns & McDonnell > 8201 Norman Center Drive > Bloomington, MN 55437 > Phone: 952.656.3652 > Fax: 952.229.2923 > [email protected] > www.burnsmcd.com > > Proud to be one of FORTUNE's 100 Best Companies to Work For > *Registered in: MN > > > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Thomas > Watt > Sent: Thursday, September 05, 2013 9:28 AM > To: [email protected] > Subject: Re: removing sprinkler on drop > > Im with Greg. I have reinstalled thousands of heads without issue. What is > the justification for this requirement? > > > On Thursday, September 5, 2013, Greg McGahan <[email protected]> wrote: >> its ALL ridiculous if you ask me.... >> it is a waste of resources >> >> >> On Thu, Sep 5, 2013 at 7:53 AM, Brad Casterline >> <[email protected] >> wrote: >> >>> There is wording somewhere that supports NOT... >>> >>> -----Original Message----- >>> From: Todd - Work [mailto:[email protected]] >>> Sent: Thursday, September 05, 2013 7:48 AM >>> To: [email protected] >>> Subject: removing sprinkler on drop >>> >>> I am working on a project where we have to add heads above an >>> existing ceiling on an existing system. The pendant heads are fed on swing >>> joints. >>> My >>> plan is to have them removes the drops (with sprinkler in them) >>> replace > the >>> 1" elbow with a tee and re-install the drops. The question came up >>> about replacing the pendant heads. They were not removed from the >>> pipe but the pipe with head was removed from the system. I never >>> thought about this before and can see arguments on both sides. Replace the >>> pendants or not? >>> >>> Todd G Williams, PE >>> Fire Protection Design/Consulting >>> Stonington, CT >>> www.fpdc.com >>> _______________________________________________ >>> Sprinklerforum mailing list >>> [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org >>> >>> _______________________________________________ >>> Sprinklerforum mailing list >>> [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org >> >> >> >> -- >> Greg McGahan >> Living Water Fire Protection, LLC <http://www.livingwaterfp.com> >> 1160 McKenzie Road >> Cantonment, FL 32533 >> 850-937-1850 >> fax 850-937-1852 >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org