Anytime a sprinkler is moved, it is potentially susceptible to damage, even if 
the line with an upright is backed out and left in the hanger. Or when a head 
in a flexible drop is moved from one location to the other. Do you require a 
new sprinkler every time a sprinkler is moved? Moved by how much? I think this 
comes down to practicality and risk tolerance.  

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com

On Sep 5, 2013, at 10:50 AM, "Cahill, Christopher" <[email protected]> wrote:

> Except for the part 'Only new sprinklers shall be installed' which has been 
> around for a long time.  Many would argue you have never been allowed to 
> reinstall sprinklers.  Yes, I know there is a lot of don't ask don't tell out 
> there.  Current edition provides clarification of the phrase only new 
> sprinklers shall be installed.  I don't see it as a change.  The 
> interpretation that if you pull the drop and never touch the sprinkler I'd 
> even argue is a little sketchy. The point of the new section is damage can 
> occur when you mess with the head.  If you lay the drop with a head on a 
> table or throw (carefully) in a bucket in my mind you have risked damage.  If 
> asked I'd say even in that case you need a new head per the code.  
> 
> Chris Cahill, PE*
> Senior Fire Protection Engineer 
> Burns & McDonnell
> 8201 Norman Center Drive
> Bloomington, MN 55437
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]
> www.burnsmcd.com
> 
> Proud to be one of FORTUNE's 100 Best Companies to Work For
> *Registered in: MN
> 
> 
> 
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Thomas 
> Watt
> Sent: Thursday, September 05, 2013 9:28 AM
> To: [email protected]
> Subject: Re: removing sprinkler on drop
> 
> Im with Greg. I have reinstalled thousands of heads without issue. What is 
> the justification for this requirement?
> 
> 
> On Thursday, September 5, 2013, Greg McGahan <[email protected]> wrote:
>> its ALL ridiculous if you ask me....
>> it is a waste of resources
>> 
>> 
>> On Thu, Sep 5, 2013 at 7:53 AM, Brad Casterline 
>> <[email protected]
>> wrote:
>> 
>>> There is wording somewhere that supports NOT...
>>> 
>>> -----Original Message-----
>>> From: Todd - Work [mailto:[email protected]]
>>> Sent: Thursday, September 05, 2013 7:48 AM
>>> To: [email protected]
>>> Subject: removing sprinkler on drop
>>> 
>>> I am working on a project where we have to add heads above an 
>>> existing ceiling on an existing system. The pendant heads are fed on swing 
>>> joints.
>>> My
>>> plan is to have them removes the drops (with sprinkler in them) 
>>> replace
> the
>>> 1" elbow with a tee and re-install the drops. The question came up 
>>> about replacing the pendant heads. They were not removed from the 
>>> pipe but the pipe with head was removed from the system. I never 
>>> thought about this before and can see arguments on both sides. Replace the 
>>> pendants or not?
>>> 
>>> Todd G Williams, PE
>>> Fire Protection Design/Consulting
>>> Stonington, CT
>>> www.fpdc.com
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
>> 
>> 
>> --
>> Greg McGahan
>> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
>> 1160 McKenzie Road
>> Cantonment, FL 32533
>> 850-937-1850
>> fax 850-937-1852
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to