There were "passive purge" systems installed for a while. Go to the last head, add a tee & tie it into the water closet supply line. It helped to purge the stagnate water from the sprinkler system, if I remember correctly, these were installed this way, pre-back flow requirement. This was done in the north east on 13D systems for a while, not sure if they're still installed this way.
Sent from my iPhone > On Sep 30, 2013, at 5:27 PM, Timothy W Goins <[email protected]> wrote: > > Install a BFP downstream of the fireline connection... > > "For I am not ashamed of the gospel , , because it is God’s power for > salvation to everyone who believes..." HCS Romans 1:16 > >> On Sep 30, 2013, at 4:18 PM, Gary Stites <[email protected]> wrote: >> >> Some of the water agencies are really "up in arms" about 13D systems with >> "dead ends". They are trying to limit the length of an armover etc. Any >> good literature or discussions on potability issues on "stagnate" water in >> the end of an armover, drop etc.? I have an AHJ ready to go head to head >> with a water purveyor...looking for ammunition. >> >> Gary Stites >> >> Design Manager, CAD/BIM >> >> RLH Fire Protection >> >> *[email protected]* <[email protected]>** >> >> 661-213-9379 >> >> 805-769-4626 >> >> >> RLH <http://www.rlhfp.com> >> Google+ <https://plus.google.com/101832074405776300082/posts?hl=en> >> Mr. Ricky <http://www.mrricky.net> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org