In the past, one EIFS product, trade name Dryvit as John mentioned, was tested 
and listed as an assembly through 1998. This assembly used a limited 
combustible foam plastic (Flame spread <25).  However, because of the cost, the 
foam component was changed by the manufacturer to a cheaper foam insulating 
material that was combustible.  The assembly could then not maintain its 
limited combustible listing.  

>From an insurance survey and grading perspective, an EIFS assembly is to be 
>considered combustible material unless  documentation is provided which 
>indicates that all components of the assembly, or the entire assembly, has 
>been tested and maintains a flame spread rating of 0.  If this documentation 
>is provided, it can be treated as noncombustible.

If the documentation indicates all components of the assembly, or the entire 
assembly has been tested and each has a flame spread rating of 25 or less, it 
is treated as limited combustible.  Dryvit assemblies installed prior to 1999, 
with proper documentation provided, are treated as limited combustible.

Hope this info is helpful


Salvatore J. Izzo III, P.E.
Risk Engineering Manager
Verisk Insurance Solutions - Commercial Property
Insurance Services Office
545 Washington Blvd.
Jersey City, NJ 07310 - 1686
t 201.469.2486
f 201.748.1942
c 732.533.7927
[email protected]
www.verisk.com/insurance

Verisk Insurance Solutions ● ISO | AIR Worldwide | Xactware



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of John 
Drucker - Home
Sent: Friday, October 04, 2013 12:41 PM
To: [email protected]
Subject: RE: EIFS

Ed,  Be nice to give you a definitive answer but the way products evolve I
would be remiss.  DryVit  ( http://www.dryvit.com/home/default.asp) is one
if not the largest manufacturer of EFIS, also referred to as "Outsulation".
Bottom line the manufacturer will need to provide the test data.

Hope that helps,

John Drucker, CET
Fire Protection Subcode Official
Fire / Building / Electrical Inspector
New Jersey



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ed
Kramer
Sent: Friday, October 4, 2013 12:24 PM
To: [email protected]
Subject: RE: EIFS

Thanks for graphic video lessons.  Obviously this stuff can be very nasty.

Is it safe to say that ALL EIFS systems are combustible, or do I have to
look at them on an individual basis?  

Ed Kramer
Lawrence, KS

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Smith,
Steven D. (CSFD)
Sent: Friday, October 04, 2013 11:04 AM
To: [email protected]
Subject: RE: EIFS

Some video examples (based on burning characteristics):

http://www.youtube.com/watch?v=0yQLIlIetDM

http://www.youtube.com/watch?v=acgWHjx6AzQ

http://www.youtube.com/watch?v=g-XR13bOzu8

http://www.youtube.com/watch?v=Tnz3hY1hotk

http://www.youtube.com/watch?v=zDtHi-s8wgM


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ed
Kramer
Sent: Friday, October 04, 2013 9:11 AM
To: [email protected]
Subject: EIFS

Is EIFS considered a 'limited-combustible material'  per NFPA 13?

 

Whether it's limited-combustible (or not) can have big impact while wading
through sections 8.15.1 and 8.15.7.

I've been searching on-line and haven't found a definitive answer.

 

I've seen the stuff used as the ceiling on exterior canopies (such as a bank
drive-through) and exterior entryways.

 

Ed Kramer

Lawrence, KS

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

This email is intended for the recipient only.  If you are not the intended 
recipient please disregard, and do not use the information for any purpose.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to