Mr. Phong, Removing everything before photos and notes and observations are made by experts, like at a crime scene, reduces the chance of coming to even a good, much less likely conclusion, but a partial list of likely suspects can be revealed by the timing. The report focus of 902, with a comment also about 1605. You add problems on the 14th and 22nd floors not mentioned in the report. What rooms? The report says the woman came BACK to her room to find the sprinkler running and reported it at 9:12 and that "09’14am the fire pump has been active." That seems like a pretty long lag time for start-up from a running sprinkler so I'm wondering if we having the usual problems with English verb conjugations by ESL speakers. Is 9:14 the start time or the time of the report. I think it pretty coincidental that a person entered her room just as the head let go, which is suggested by the timing of the pump start. What caused the ERT to go to 1605 within minutes of a reported discharge on the ninth floor? Waterflow from a flow switch on 16, a guest report or something else? Maybe not pertinent, but maybe it is. And why aren'r floors 14 and 22 mentioned in the report when there is the one mention of 1605 amongst all the information about 902? How often is the pump tested. If on a regular basis and the discharge was initiated by a faulty head opening which caused three more to open when the pump kicked in, more likely than four heads opening at the same time for no obvious reason, why did four fail simultaneously on multiple floors that have had pressure regulating valves at least through fourteen if twenty-two is the highest floor? Too many coincidences, even though, with the limited information, one head opening is the cause for the others to follow. Could just be that all four sustained some sort of damage at one time, either at installation or after, and then the one failed and the pump start stressed the other three to the point of failure. Could be the guest accidentally caused the first event, was afraid of getting in trouble and lied about coming back to the room to find the sprinkler running. Was the guest wet? If no it would suggest she was telling the truth as no one would enter the room far enough to get drenched, but if she was that would mean she was near the head when it discharged. And that type of head could easily be damaged to the point of discharge by a hanger as well as a thrown object. I'm not suggesting she threw a bowling ball at it as in the video but the hardwood floor at the YMCA I go to was ruined by a racquetball ball hitting a fully concealed sprinkler head on the at least 16 foot high ceiling. I personally know of one semi-recessed head similar to the Victaulics you have that was set off in a hotel by a couple of guessing playing catch with a tennis ball, and of course numerous known discharges from people hanging clothes from sprinklers, all installed near the ceiling. The second link is a representative sample of a sign I increasingly see in hotels. This would not be everywhere if the problem were not common.
http://www.youtube.com/watch?v=Hv3v7c_OHOw http://2.bp.blogspot.com/-Y2VH4T-7rdU/TvCHvTwTPqI/AAAAAAAAADo/RwFQH0I3Tig/s1600/sprinkler.gif On Sat, Oct 5, 2013 at 6:33 AM, Phong - Indochine Engineering < [email protected]> wrote: > Thanks Dwight, > > It is at high level. > But if it happened with a light clothe, should be no problem with the > metallic side cover? > > http://static.victaulic.com/assets/uploads/literature/40.11.pdf > > > Regards, > Le Vu Phong > Mobile: +84 (0) 902 363 525 > > > > > > > phong_indochineengineering > > > > -----Original Message----- > From: [email protected] [mailto: > [email protected]] On Behalf Of Dwight Havens > Sent: Saturday, October 05, 2013 7:29 PM > To: [email protected] > Subject: Re: Sprinkler broken in 05 star hotel guest rooms > > My first attempt didn't get through, but have you considered the common > practice by patrons of hanging clothing on hangers from the sidewall > sprinklers? > > Dwight > > > > ________________________________ > From: Charles Thurston <[email protected]> > To: Phong - Indochine Engineering <[email protected]> > Sent: Saturday, October 5, 2013 8:24 AM > Subject: Re: Sprinkler broken in 05 star hotel guest rooms > > > Hello Phong, > > What is the pressure in the standpipe feeding these when the fire pump is > at churn? > > From the Victaulic cut sheet for this head: > Max. Working Pressure: > 175 psi/1200 kPa FM Global > 250 psi/1725 kPa UL > Factory Hydrostatic Test: 100% @ 500 psi/3450 kPa > > > Also a chance the heads were hit with something during construction after > they were installed, Or the installer could have dropped a head. > > Saturday, October 5, 2013, 6:35:07 AM, you wrote: > > > The model of the head is V2710 (K5,6) of Victaulic > > > > Regards, > > Le Vu Phong > > Mobile: +84 (0) 902 363 525 > > > > > > > > > phong_indochineengineering > > > > > -----Original Message----- > > From: [email protected] > > [mailto:[email protected]] On Behalf Of > Phong - Indochine Engineering > > Sent: Saturday, October 05, 2013 5:29 PM > > To: [email protected] > > Subject: RE: Sprinkler broken in 05 star hotel guest rooms > > > But it is still a chance that during the construction, some heads are > installed by another brand... > > > > Regards, > > Le Vu Phong > > Mobile: +84 (0) 902 363 525 > > > > > > > > > phong_indochineengineering > > > > > -----Original Message----- > > From: [email protected] > > [mailto:[email protected]] On Behalf Of > Phong - Indochine Engineering > > Sent: Saturday, October 05, 2013 5:06 PM > > To: [email protected] > > Subject: RE: Sprinkler broken in 05 star hotel guest rooms > > > Exactly Steven. > > > > Regards, > > Le Vu Phong > > Mobile: +84 (0) 902 363 525 > > > > > > > > > phong_indochineengineering > > > > > -----Original Message----- > > From: [email protected] > > [mailto:[email protected]] On Behalf Of > Steven Scandaliato > > Sent: Saturday, October 05, 2013 4:50 PM > > To: [email protected] > > Subject: RE: Sprinkler broken in 05 star hotel guest rooms > > > So I am assuming each floor is fed from the same standpipe and > > supplied by the same fire pump...and the same sprinkler head type from > same manufacturer?? > > > Steven Scandaliato, SET CFPS > > 520.971.2322 Cell > > > > -----Original Message----- > > From: [email protected] > > [mailto:[email protected]] On Behalf Of > Phong - Indochine Engineering > > Sent: Saturday, October 05, 2013 3:47 AM > > To: [email protected] > > Subject: RE: Sprinkler broken in 05 star hotel guest rooms > > > Thanks Steven, > > > The rooms are on different floors: L9, L14, L16, and L22. > > > Regards, > > Le Vu Phong > > Mobile: +84 (0) 902 363 525 > > > > > > > > > phong_indochineengineering > > > > > -----Original Message----- > > From: [email protected] > > [mailto:[email protected]] On Behalf Of > Steven Scandaliato > > Sent: Saturday, October 05, 2013 4:46 PM > > To: [email protected] > > Subject: RE: Sprinkler broken in 05 star hotel guest rooms > > > Le Vu, > > Can you tell me, were the sprinklers that activated in consecutive > > rooms...side by side or one right next to the other or are they on > > different floors or at different locations on the same floor? > > > > Steven Scandaliato, SET CFPS > > 520.971.2322 Cell > > > -----Original Message----- > > From: [email protected] > > [mailto:[email protected]] On Behalf Of > Phong - Indochine Engineering > > Sent: Saturday, October 05, 2013 3:08 AM > > To: [email protected] > > Subject: Sprinkler broken in 05 star hotel guest rooms > > > Hello, > > > In a 04 year old 05 star hotel of Starwood in Asia, recently side > > wall sprinklers of 03 different guest rooms are broken with unknown > > reasons in the morning about 10am. There is no fire at all. What are > > all brainstormed possible reasons? > > > Typical report of the scenes: > > > 09’14am the fire pump has been active. Security and engineering has > responded to check. > > - 09’14am Mr. Kiet (Bellman) informed to GSC to raise code 888 – > > since he has been informed by Guests (R.092) that the water came > > out in her room and her properties were wet. > > - 09’16am at the scene Mr. Trung discovered sprinkler in R.902 was > > broken and the water came out immediately he turned off the power in > > R.902 and closed the valve of the pipe > > - 09’18am ERT team came to the R1605 ERT focused on clearing the > > water and removing all items from the room. > > - 09’18am Mr. Huy (Duty Manager) & Ms. Kieu (Assistant Housekeeping > > Manager) assisted Guests to move to R.920. > > - 09’21am Management team responded to the scene, calm down the > > guest and we have listed the wet items to send for washing & drying (see > below list) > > - 12’30pm Mr. Sinh (Maintenance manager) replaced sprinkler and smoking > detector in R902 > > > > Information from Guests (R0902): > > 9’12am: When Guest came back room 0902, they discovered the > > sprinkler released and water came out in their room. Then Ms. Jiang > > Yuting went to in front of lifts lobby and reported to Mr. Kiet(Bellman) > about this case > > > > > Regards, > > Le Vu Phong > > Mobile: +84 (0) 902 363 525 > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > > > -- > Best regards, > Charles mailto:[email protected] > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org