2013-11.2.3.2.3.1  (4) ..no unprotected ceiling pockets as allowed by 8.6.7 & 
8.8.7 exceeding 32 sq. ft. (to tie in the previous question)

Ceiling pocket definition 2013-3.3.4 & the Annex (not enforceable, I know) 
speaking to intent of the definition, and specifically addressing QR reduction 
and how it is not to be used for structural members(the definition).. This was 
added in the 2013 edition, the 2010 edition only speaks to application to 
obstructed/unobstructed and not the QR reduction.

So a ceiling pocket cannot be defined by obstructed construction.  So you 
comply with the QR rules?

Am I following that correctly?

DW

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve 
Leyton
Sent: Tuesday, October 15, 2013 2:06 PM
To: [email protected]
Subject: RE: QR Reduction for Obstructed Construction

Does it say that it can't?   We take it in attics all the time ... 

Steve L




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, October 15, 2013 1:46 PM
To: [email protected]
Subject: QR Reduction for Obstructed Construction

I asked once before about ceiling pockets vs. beam pockets and didn't get a 
nibble so I'll try a slightly different twist on the question. Can the QR 
reduction be applied to obstructed construction? Can the reduction be taken for 
twin tee construction?

Ron F

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to