Isn't the thrust restraint a requirement for systems with pressures in excess 
of 100 psi?

----- Original Message -----
From: Ron Greenman [mailto:[email protected]]
Sent: Sunday, October 20, 2013 09:42 PM
To: [email protected] 
<[email protected]>
Subject: Re: NFPA 13 '10 9.3.6 BL Restraint

Don't have anything at the moment. Is this eq country? Somewhere there's 
something that requires up thrust restraint at the end of line. I think lateral 
is only required for seismic areas, but I'd need to read the section before I 
made an unequivocal statement. No books in the car. 

Sent from my iPhone

> On Oct 20, 2013, at 2:08 PM, "Cahill, Christopher" <[email protected]> 
> wrote:
> 
> Got a code section that connects a length of a BL to a restraint or the 
> inverse of what you said, that if it needs a hanger then it needs restraint?  
> I got one that says it doesn't, 9.3.6.7 Drops and armovers shall not require 
> restraint. 3.5.3 Arm-Over. A horizontal pipe that extends from the branch 
> line to a single sprinkler or a sprinkler above and below a ceiling. I just 
> find it odd I can have a 2" pipe 100' long serving one head and it doesn't 
> need anything but regular old gravity hangers.  Or I can't find anything to 
> challenge 9.3.6.7.  My case I have a bunch of 3-8'  1" legit armovers.  
> Contractor didn't install restraint and I think he's right technically. 
> 
> Chris Cahill, PE*
> Senior Fire Protection Engineer 
> Burns & McDonnell
> 8201 Norman Center Drive
> Bloomington, MN 55437
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]
> www.burnsmcd.com
> 
> Proud to be one of FORTUNE's 100 Best Companies to Work For
> *Registered in: MN
> 
> 
> 
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of 
> rongreenman .
> Sent: Sunday, October 20, 2013 2:19 PM
> To: [email protected]
> Subject: Re: NFPA 13 '10 9.3.6 BL Restraint
> 
> Restraint is to avoid upward thrust and side to side thrust, whipping for 
> Devo fans, at the end of a branch line. If an armover does not need a  hanger 
> it wouldn't need restraint
> 
> 
> On Sun, Oct 20, 2013 at 7:50 AM, Cahill, Christopher
> <[email protected]>wrote:
> 
>> Two questions.
>> 
>> Is there a length of an armover that needs restraint?  Imagine a 12'
>> armover that only feeds one head.
>> 
>> Can restraint be connected to something other than structure, like a 
>> concrete floor above?
>> 
>> Chris Cahill, PE*
>> Senior Fire Protection Engineer
>> Burns & McDonnell
>> 8201 Norman Center Drive
>> Bloomington, MN 55437
>> Phone:  952.656.3652
>> Fax:  952.229.2923
>> [email protected]<mailto:[email protected]>
>> www.burnsmcd.com<http://www.burnsmcd.com/>
>> 
>> Proud to be one of FORTUNE's 100 Best Companies to Work For 
>> *Registered in: MN
>> 
>> 
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
> 
> 
> 
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
> 
> [email protected]
> 
> http://www.bates.ctc.edu/fireprotection/
> 
> 253.680.7346
> 253.576.9700 (cell)
> 
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> 
> They are happy men whose natures sort with their vocations. -Francis Bacon, 
> essayist, philosopher, and statesman (1561-1626) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to