I have always thought it ironic that we spend so much of our time trying to do 
a correct installation based on the standards while the standard we use for ITM 
has us ignore the correctness of the original/current installation. 25 probably 
should have been NFPA 22 instead (Catch 22).

I just looked at building that was written up by a city inspector. The place 
has been there doing the same thing in this 30k sqft. building for over 20 
years. They have an OH2 pipe schedule wet system with rolls of bubble wrap 
stored on end to 20 ft. and bags of polystyrene peanuts 3' in diameter and 10' 
long piled on top of each other to about 18' high. There are also inverted 
pyramid shaped canvas type bags 10'x10' at the top that are about 20' deep with 
spout at the bottom. They are full of peanuts. What would an NFPA 25 inspection 
report say about this building?

Seems impossible to fix. Even if we reported infractions to the AHJ they would 
have to glean form 1000's of reports the partially obstructed LH sprinkler from 
the 30,000 sqft of exposed expanded plastic stored 20' high under an OH system.

Ron F


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Cahill, 
Christopher
Sent: Wednesday, November 06, 2013 3:15 PM
To: [email protected]
Subject: RE: NFPA25 scope

I think all would agree with what you said.  I think the question asked was 
woulda, coulda, shoulda NFPA add system evaluation?

Roland's question was 'One of the question is should verifying the adequacy of 
the sprinkler system be part of an NFPA 25 inspection or some other NFPA 
document?'

Chris Cahill, PE*
Senior Fire Protection Engineer
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in: MN




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Jim 
Davidson
Sent: Wednesday, November 06, 2013 3:17 PM
To: [email protected]
Subject: RE: NFPA25 scope

To all,

NFPA 25 is a document that defines what the committee has defined what is the 
minimum level of testing, inspection and maintenance is required of water based 
fire protection systems as defined in the scope of the document "1.1 Scope. 
This document establishes the minimum requirements for the periodic inspection, 
testing, and maintenance of water-based fire protection systems, including 
land-based and marine applications."   Paragraph 1.1.2 further defines scope 
"The types of systems addressed by this standard include, but are not limited 
to, sprinkler, standpipe and hose, fixed water spray, and foam water. Included 
are the water supplies that are part of these systems, such as private fire 
service mains and appurtenances, fire pumps and water storage tanks, and valves 
that control system flow. The document also addresses impairment handling and 
reporting. This standard applies to fire protection systems that have been 
properly installed in accordance with generally accepted practices. Where a 
system has not been installed in accordance with generally accepted practices, 
the corrective action is beyond the scope of this standard. The corrective 
action to ensure that the system performs in a satisfactory manner shall be in 
accordance with the appropriate
installation standard." 

There are no NFPA standards that require a legally (properly permitted and 
properly designed to the legal standard at time of installation) installed 
sprinkler system to be upgraded when the standards change. What are we trying 
to do, make sprinkler contractor's and inspection contractor's liability 
insurance unaffordable, and a new profit stream for the legal community. It is 
not the job of the inspecting contractor to fix the problems of the original 
sprinkler system approval process misadventures. Design problems should be pick 
up during the approval process and system acceptance testing by the AHJ or 
their representatives along with the Owners design team.    The evaluation of 
the sprinkler system design vs occupancy classification can be done legally at 
time of building or tenant occupancy change by the AHJ in accordance with the 
codes. 

Your inspection reports are being sent to the owner, in a separate letter to 
the Owner the contractor should note that there has been a reduction in the 
pressure/flow of the water supply since the last flow test. The same applies to 
fire pump test etc., the problems with changes in storage is a change in 
occupancy classification and should be addressed by the AHJ at the time of 
occupancy change. 

The redrawing of the systems and recalculation of the system is the work of the 
owner's fire protection engineer not a sprinkler contractor but if the 
contractor wants to play engineer go ahead but do not say after the fact "I am 
not an engineer but a contractor, I'm not liable."     

The bad sprinkler systems installations are why more jurisdictions are looking 
at contractor licensing laws.  

Regards

Jim
    

DAVIDSON ASSOCIATES

Fire Protection Engineering     P. O. Box 4010
Code Consultants        Greenville, DE  19807-0010
Medical Gas Systems Engineering (302) 994-9500
        Fax (302) 234-1781

CONFIDENTIALITY
This report and any attachments are confidential and also may be privileged.
If you are not the named recipient, or have otherwise received this report in 
error, please destroy the report, notify the sender immediately, and do not 
disclose its contents to any other person, use them for any purpose, or store 
or copy them in any medium.
Thank you for your cooperation.

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Cahill, 
Christopher
Sent: Wednesday, November 06, 2013 2:15 PM
To: [email protected]
Subject: RE: NFPA25 scope

Absolutely, but I see a lot of issues that CLEARLY need to be spelled out in 
GREAT detail.  No place for wishy-washy language that lawyers will use against 
contractors.

Some examples of issues to tackle:

Change in water flow tests. Well, do I even need a test?  Current argument 
about backflows and whether there needs to be measurements.  Most AHJ's expect 
hose monsters.

Change in codes that change the design even though the occupancy has not 
changed. I have a hangar built for 2-747's to the 1967 NFPA 409.  Guess what, 
foam is not required but today not possible without foam.  We've learned about 
storage. We used to have 3 OH curves.  

Speaking of storage I went through this as an AHJ a lot in the 90's.  We asked 
those with high-piled storage to prove they had not changed their height or 
commodities from the original install and the original install met the codes at 
the time.  Because if you didn't change you were deemed compliant by the code 
at least.  Almost, none could prove they complied.  Seemed up to about 16' 
class III was ok but higher, tires or plastics seems to fail. 

We all know there are a lot of deficient installations.  What do we do with a 
year old system that won't work for whatever reason?

How about obstruction issues?

And much of the original designs are lost about a week after occupancy.  Are we 
tracing pipe?  Re-doing calcs for old system.  

And we all know really bad installations put out a lot of fire as long as the 
valve is open.  My recollection is if the valve is open and no one interferes 
in the operation during the fire NFPA stats are 97% successful?  Sorry, been a 
while since I read the report.  If this effort would only deal with the 
remaining 3% is it worth it?  Perhaps this should start as a targeted approach, 
hospitals, nursing homes and schools?  Although, one of my kids just started 
high school, building isn't that old.  I've only been there a couple times and 
each time I see a spacing or obstruction deficiencies.  I can only imagine what 
a review of the calc's and pipe size would reveal.  Am I concerned, only a 
little, see first sentence of this paragraph. Maybe storage?   You'll note I 
didn't say residential yet.  IMHO it's even harder to screw those up such to 
create a risk.  Yes, I know it can be done!

Don't get me wrong I believe existing systems should get a good review at some 
point.  NFPA 25 is already felt to building owners to be a money grab for 
contractors.  Telling them I need to spend 100's of hours redrawing and 
re-calc'ing a system will result in revolt. Then I tell them the original 
installation didn't meet code, then they need a pump because water decayed.....

Chris Cahill, PE*
Senior Fire Protection Engineer
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in: MN




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Roland 
Huggins
Sent: Wednesday, November 06, 2013 9:13 AM
To: [email protected]
Subject: Re: NFPA25 scope

ACtually this issue is much broader than NFPA 25.  NFPA is asking the question, 
what if anything that it do to reduce the number of failures of the sprinkler 
system to control the fire (due to changes of contents changes in the water 
supply, etc where the water discharge is not enough to control the fire).  One 
of the question is should verifying the adequacy of the sprinkler system be 
part of an NFPA 25 inspection or some other NFPA document?

That is the starting point for this thread.  What do you gals and guys think?

Roland

Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Nov 5, 2013, at 10:09 PM, "Douglas Hicks" <[email protected]> wrote:

> http://www.nfpa.org/newsandpublications/nfpa-journal/2013/november-dec
> ember-2013/features/closer-look?order_src=C246
> 
> More on 25 and the scope of 25.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to