Right on Travis.
Ron F

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Travis Mack
Sent: Wednesday, December 11, 2013 4:33 PM
To: [email protected]
Subject: Re: EQ Bracing

I believe I know what jurisdiction Ron F is talking about.  I have explained to 
their reviewers that per the IFC that they have adopted, bracing is not 
required in Seismic Design Category A/B.  I ask for a reference as to where it 
is required.  I get pointed to Chap 9 of NFPA 13.  I get told that this is the 
way we do it and it has to be done this way or it won't get approved.  After 
awhile, your head gets flat from beating it against the wall so much and you 
just comply.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

On 12/11/2013 4:28 PM, Rod DiBona wrote:
> Ron,
>
> Curious ... " because they can..." Does that mean that they have a local 
> amendment, are using the IFC catchall that they can do what they think ( 
> appendix clearly shows that wasn't intent but is used as a hammer) or does it 
> mean it isn't worth the fight because you may win the battle in court but 
> lose the war for the next 20 years you work in their area?
>
> Rod at Rapid
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of 
> [email protected]
> Sent: Wednesday, December 11, 2013 12:54 PM
> To: [email protected]
> Subject: RE: EQ Bracing
>
> They make us install sway braces in a non-seismic zone because they can. We 
> ask if they want calc's and the answer is what calc's? Were just trying to 
> get by. We also put $5k worth of overfill protection on a 180 gallon diesel 
> fuel tank in a pump room, because they make us. Pretty hard to justify either 
> one.
> Ron F
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of 
> Steve Leyton
> Sent: Wednesday, December 11, 2013 11:32 AM
> To: [email protected]
> Subject: RE: EQ Bracing
>
> Drive screws? Lags are no longer allowed because they pull out. Drive screws 
> are ... negligent, arguably.
>
> Forest - all I can say about your spacing template is that it's five editions 
> old and any BO that accepts it isn't doing the due diligence.
>
> Steve Leyton
>
> -------- Original message --------
> From: [email protected]
> Date:12/11/2013  10:16 AM  (GMT-08:00)
> To: [email protected]
> Subject: RE: EQ Bracing
>
> We have jurisdictions in AZ that require what we call "feel good bracing".  
> No calc's required, use drive screws to attach brace from 8" pipe to wood 2x6 
> at the roof. A little different from the hoops we jump through for OSHPAD in 
> CA.
> Ron F
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of 
> Steve Mackinnon
> Sent: Wednesday, December 11, 2013 10:55 AM
> To: [email protected]
> Subject: RE: EQ Bracing
>
> What is the difference?
>
> Steven MacKinnon
> Fire Protection Division
> Hartcorn Plumbing and Heating, Inc.
> 850 South Second Street
> Ronkonkoma, NY 11779
> Office 631-580-2300  Fax - 631-580-1090
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of 
> rongreenman .
> Sent: Wednesday, December 11, 2013 12:47 PM
> To: [email protected]
> Subject: Re: EQ Bracing
>
> That doesn't work in seismic zones Forest. That's sway bracing, not seismic 
> bracing.
>
>
> On Wed, Dec 11, 2013 at 7:30 AM, Forest Wilson Fire Sprinkler Contractor < 
> [email protected]> wrote:
>
>> Keep simple?
>> 4 way every change of direction.
>> Longitudinal every 80.
>> Latitudes every 40.
>> Flexible couplings top and bottom of riser.
>>
>> These guidelines will satisfy most building departments.
>> Some will want calculations etc.
>>
>>
>> Forest Wilson
>> Fire Sprinkler Contractor
>> 937-736-0425
>>
>> Notice:
>> This message is confidential. It may also be privileged or otherwise 
>> protected by work product immunity or other legal rules. If you have 
>> received it by mistake, please let us know by e-mail reply and delete 
>> it from your system; you may not copy this message or disclose its 
>> contents to anyone. Please send us by fax any message containing 
>> deadlines as incoming e-mails are not screened for response deadlines.
>> The integrity and security of this message cannot be guaranteed on the 
>> Internet.
>>
>> -------- Original message --------
>> From: JD Gamble <[email protected]>
>> Date:12/10/2013  4:58 PM  (GMT-05:00)
>> To: [email protected]
>> Subject: EQ Bracing
>>
>> What are the best "Keep It Simple Stupid" resources for seismic 
>> applications?
>>
>> And, ... is EQ bracing limited to only those floors above grade?
>>
>>
>>
>> JD Gamble
>> Life Safety Solutions of Sheridan
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> l er.org _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> l
>> er.org
>>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>
> They are happy men whose natures sort with their vocations. -Francis 
> Bacon, essayist, philosopher, and statesman (1561-1626)
>
> A problem well stated is a problem half solved. -Charles F. Kettering, 
> inventor and engineer (1876-1958) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to