Quick question I have been wanting to ask for about 20 years now:
If you are/were an AHJ would you accept the calculation of the required
section modulus based on say, 10 feet of water-filled pipe, instead of 15
feet, without requiring a Structural P.E. stamp? Same question for hanging
pipe type other than S10 or S40, or available section modulus for other than
S10 or S40. Since section modulus = moment/stress, the calculations are far
simpler than hydraulic calculations (i.e. double the span = double the
required section modulus, etc). I have never designed a trapeze member other
than S10 or S40 at 15' apart, I guess because I thought it would not be
worth the aggravation it might cause me.

thanks,
Brad  