just for info, I was going to ask this question last June, but the thread got a bit of track-- i wrote:
section modulus is moment divided by stress. moment is half the force(lb) times half the distance(in). the force is the weight of the water-filled pipe plus 250. the distance is 4ab/a+b. the stress is 15,000. for example: 4" S40 15 feet, center of 48" span: 16.4 x 15 = 246 + 250 = 496 x .5 = 248 4 x 24 x 24 = 2304 / 48 = 48 x .5 = 24 248 x 24 = 5952 / 15,000 = .3968 Brad If someone wants to make their own spread sheet, NFPA 13 uses a weight density of 490 lb/ft3 for steel and 62.4 lb/ft3 for water. One can subtract the volume based on the I.D. from the volume based on the O.D. to get the weight/ft of the steel and use the I.D. volume for the weight/foot of the water. -----Original Message----- From: Brad Casterline [mailto:[email protected]] Sent: Wednesday, January 15, 2014 12:00 PM To: [email protected] Subject: RE: trapeeze member sizing program Quick question I have been wanting to ask for about 20 years now: If you are/were an AHJ would you accept the calculation of the required section modulus based on say, 10 feet of water-filled pipe, instead of 15 feet, without requiring a Structural P.E. stamp? Same question for hanging pipe type other than S10 or S40, or available section modulus for other than S10 or S40. Since section modulus = moment/stress, the calculations are far simpler than hydraulic calculations (i.e. double the span = double the required section modulus, etc). I have never designed a trapeze member other than S10 or S40 at 15' apart, I guess because I thought it would not be worth the aggravation it might cause me. thanks, Brad _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org