Thanks Charles, good point. I guess if I did my job as a tech correctly fitters 
would not need anything other than the shop drawings. Still, if it was split, I 
envision the one called 'installation' as the one with the tables and nothing 
open to interpretation, not full of exceptions and references to other sections 
or codes, etc . The one called 'design' would not have the tables but the 
straight up simple formulas that produce the tables. I hope this makes sense as 
an example of what I am thinking. It seems that 13 is becoming almost 
hopelessly complicated for everyone and anything that could be done to sort it 
out would be a good thing.
Thanks again Charles.
wbr, Brad.

> On Jan 19, 2014, at 6:31 AM, Charles Thurston <[email protected]> wrote:
> 
> Hello Brad,
> 
> I dis-agree with splitting them. If you do not know how to install it, You 
> sure da heck can't tell someone else how to install it. In 35 years on and 
> around construction, I have seen many many buildings designed (with details) 
> that can not be built the way they were designed. Is that what our industry 
> wants for Fire Sprinklers?
> 
> Saturday, January 18, 2014, 9:40:52 PM, you wrote:
> 
>> I remember when fitters knew 13 as well or better than designers.
>> The schedules and tables were essential then, because handheld
>> calculators were not prevalent- 13 was a Field Guide for
>> installation. This is not the case anymore. What should we do? Split DESIGN 
>> from INSTALLATION?
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> 
> 
> -- 
> Best regards,
> Charles Thurston                          mailto:[email protected]
> Systems Design Manager
> NICET Certified
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to