I would recommend to everyone the website www.nfpa.org/antifreeze.  There is a 
lot of good information and a video by Matt Klaus that discusses the antifreeze 
story should be helpful.

This leads me to the risk assessment. There were some very interesting test 
results from the various tests of sprinklers in various scenarios with 
different heights, pressures, orifice size etc. A risk assessment would allow 
you to take these results and apply them to a particular site.  This of course 
would have to be approved by AHJ.  A PE is not required but I would recommend 
an FPE who understands the tests results.

Happy winter to all......

Top Myers
RelMark Group
961 Pottstown Pike
Chester Springs, PA 19425
610-321-2415 X-219   Cell 610-952-0965
[email protected]


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Jay Stough
Sent: Monday, January 27, 2014 1:58 PM
To: Sprinkler Forum
Subject: NFPA 25 & Antifreeze

I was just rereading NFPA 25 (2014) 5.3.4 and specifically 5.3.4.2.1 and if I 
am reading it correctly, if the antifreeze is a type that is not acceptable, it 
must be drained and replaced.  But if you look at 5.3.4.2.1, there are three 
criteria that you have to meet in order to use the premixed antifreeze, 
including a risk assessment.  Has anyone done this risk assessment as shown in 
the annex?


--
*Jay Stough*
 SET, CFPS
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to