I found the report fascinating.
Table 1 (test matrix) shows only (2) scenarios with the 1.4 MW Heat Release
Rate, the rest being 3.0 MW. 1.4 MW= 1,400 kW, 14,000 'one hundred watt'
light bulbs, (3) big dry Christmas trees. And the test were not meant to
apply to non-residential!
Any way I need to re-read it but, Jerry, it was almost as if everyone got to
the point where they were saying "for crying out loud, how big we gotta make
this fire to burn some antifreeze here"?
Seriously though, the things Cecil and Top mentioned all sort of works
together for RISK, I just wish that out of the (15) test scenarios, (2) were
the 3 meg and (13) were the 1.4 meg instead of the other way around.

Brad Casterline 

-----Original Message-----
From: [email protected] [mailto:[email protected]] 
Sent: Tuesday, January 28, 2014 9:13 AM
To: [email protected]
Subject: Re: NFPA 25 & Antifreeze Comment(s)

Good morning to All:


I have read much about anti-freeze and appreciate having received very
valuable info (and advice) from this Forum. After nearly 40 years in this
'biz', I have come to respect the opinions and shared knowledge of my
sprinkler colleagues. That said...



We continue to design anti-freeze systems, typically with CPVC/glycerin
applications. Why? Well, for one, some of our Clients require it, to wit: We
have a current Client - I have mentioned him before in this Forum - who
refuses to have dry-pipe systems installed in his buildings. This is a
well-informed billionaire who knows what he wants, and he is going to get
what he demands. Other Clients have similar reservations and, after much
dialogue, we proceed with the glycerin systems.



I/we fully recognize that no amount of written agreements and/or
'understandings' mean much once it goes in to a court of law. I do rely
heavily on the early results Russ Fleming gave us at an NFSA/ Puget Sound
meeting a few years back: the anti-freeze flash/explosion scenario could not
be replicated in laboratory settings when one of three items were removed
from the test protocol: high system pressures (100+ psi?), small orifice/2.8
K, elevated levels of glycerin/glycol. I believe there is a reason these
"mishaps" with anti-freeze are so rare - and I believe the aforementioned
test results play a major part in the equation.




Proceeding with caution is always advisable in our business/profession. I
have been designing anti- freeze systems (primarily in homes/13'D') and have
yet to experience problems beyond thread leaks. Call me foolish, lucky,
naive, reckless - our Clients are fully informed before the decision is made
to go with anti-freeze and we get it in writing and submit the forms to our
attorneys. This is how we do it and will continue as long as the AHJ and our
FPE's 'endorse' it.


Okay - I'm ready for the "feedback" (blow-back??) And, yes, Cecil/Top: I
have 50/50 "field-mixed" glycerin in my CPVC sprinkler system in the home we
built 10+ years ago here in Santa Fe - and we do not have commercial-type
cooking equipment in our kitchen...


Gracias from Nuevo Mejico!!


Jerry
[email protected]


Jerry D. Watts, SFPE
President & Co-Founder
ACCENT FIRE ENGINEERING INT'L. Ltd.
Santa Fe, New Mexico USA
(800) 503.1961






-----Original Message-----
From: Top Myers <[email protected]>
To: sprinklerforum <[email protected]>
Sent: Mon, Jan 27, 2014 6:52 pm
Subject: RE: NFPA 25 & Antifreeze


I would recommend to everyone the website www.nfpa.org/antifreeze.  There is
a 
lot of good information and a video by Matt Klaus that discusses the
antifreeze 
story should be helpful.

This leads me to the risk assessment. There were some very interesting test 
results from the various tests of sprinklers in various scenarios with
different 
heights, pressures, orifice size etc. A risk assessment would allow you to
take 
these results and apply them to a particular site.  This of course would
have to 
be approved by AHJ.  A PE is not required but I would recommend an FPE who 
understands the tests results.

Happy winter to all......

Top Myers
RelMark Group
961 Pottstown Pike
Chester Springs, PA 19425
610-321-2415 X-219   Cell 610-952-0965
[email protected]


-----Original Message-----
From: [email protected]
[mailto:[email protected]] 
On Behalf Of Jay Stough
Sent: Monday, January 27, 2014 1:58 PM
To: Sprinkler Forum
Subject: NFPA 25 & Antifreeze

I was just rereading NFPA 25 (2014) 5.3.4 and specifically 5.3.4.2.1 and if
I am 
reading it correctly, if the antifreeze is a type that is not acceptable, it

must be drained and replaced.  But if you look at 5.3.4.2.1, there are three

criteria that you have to meet in order to use the premixed antifreeze, 
including a risk assessment.  Has anyone done this risk assessment as shown
in 
the annex?


--
*Jay Stough*
 SET, CFPS
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to