read the paragraph again slowly. It’s quite explicit and literal.  If someone 
you know is not allowed to give you a little grieve - lol.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Jan 28, 2014, at 1:27 PM, Todd - Work <[email protected]> wrote:

> IF I could get a clarification on something. I am working on a project where 
> we have a piece of 18" spiral duct that is obstructing some future sidewall 
> sprinklers. Section 8.7.5.2.1.3 talks about the 3x rule. That would require 3 
> x 18" or 54" clearance. However, it also says the maximum clear distance 
> required shall be 24". The associated figure doesn't exactly clarify it. 
> Which distance needs to be maintained, 54" or 24"? It's a pretty big 
> disparity and would have a big impact on the shadow. At present, the distance 
> will be about 17". 
> 
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> www.fpdc.com
> 860-535-2080 (ofc)