Nope, not a game. Last night I wondered if the death you mentioned was cited in 
Chris Cahill's recent Death By Sprinkler thread (I could not remember).
Jerry mentioned 'independent studies' in one of his posts. I hope we get more 
of those before 2022.

> On Jan 29, 2014, at 6:00 PM, "Steve Leyton" <[email protected]> 
> wrote:
> 
> I'd add that if you think that you can extinguish any fire with 100% AF,
> whether your shop drawings were well-executed or not, you are very
> wrong.  Having seen several of UL's fire test videos from the NFPARF
> anti-freeze project in committee, I assure you that high concentrations
> of Glycol are very flammable,  and undiluted it's an accelerant.   This
> isn't a game; somebody died from a flameout due to +70% glycol.   The
> consensus reaction (some would say "overreaction") by NFPA's Codes and
> Standards Council, sprinkler correlating committee and the affected 13's
> was to ban the stuff, which leaves a lot of new construction hanging in
> the void and many, MANY existing systems in limbo.  Our state fire
> marshal in CA was troubled enough by this that our OSFM NFPA 25 task
> group was charged with coming up with a means of safely maintaining
> anti-freeze as she (rightly, in my mind) foresaw another sprinkler issue
> that could strain the credibility of our industry and could undermine
> the residential sprinkler mandate.   We are moving forward with proposed
> language for our state ITM standard that says, essentially, that with
> existing AF you are to ID what it is and if it's banned or in too heavy
> a concentrate, drain and discard.  Maintenance and refills are to
> utilize only pre-mix and only conservative lower concentrations.  It's
> not required to be non-flammable or listed, just low concentrations.
> I'd publish the numbers but it's all draft language so please don't ask
> for it yet.   It will be going public in the next few weeks.
> 
> Yes, it's flawed and yes, there are likely some locales where it's not
> enough protection for frigid temps.  But this is, after all, California
> <chuckle, chortle, pass the sunscreen>.
> 
> Steve  
> 
> 
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> Roland Huggins
> Sent: Wednesday, January 29, 2014 3:48 PM
> To: [email protected]
> Subject: Re: NFPA 25 & Antifreeze Comment(s) RETORT
> 
> BE cautious when saying mix it yourself out loud.  The standards (both
> 13 and 25) require only factory premixed solutions to be used.  You're
> also suppose to drain the system then refill it.  Combine that with the
> cost of back flow preventers and expansion chambers and AF system are
> not very appealing.
> 
> Roland
> 
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org
> 
> 
> 
> 
> 
> On Jan 29, 2014, at 3:19 PM, Andy-Johnston <[email protected]>
> wrote:
> 
>> Even when you mix it your self, you mix it up real good in a seperate
> barrel, check it, then pump it in. I wonder If people trying to do the
> math and pumping in the antifreeze followed by the water contributed o
> the problem?
>> Andy
>> 
>> --
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to