Just glanced at the report.  According to the abstract, it self extinguishes if 
the tree is not allowed to dry and and maintains a moisture content in the 
needles in excess of 100%.  How does one exceed 100%?

The fire size for a dry tree was 3.2MW to 4.3MW with the needles consumed 
within 60 seconds.  I remember the tree I fired-up in the backyard as a kid 
went off like gasoline and gone in like 30 seconds.  Nonetheless, the fire size 
for most of us would be much bigger cause the study used a fairly small tree 
about 6 ft tall.

Good to see that a residential sprinkler contained such an aggressive fire.

 
Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Jan 31, 2014, at 7:14 AM, Brad Casterline <[email protected]> wrote:

> Impact of a Residential Sprinkler on the
> 
> Heat Release Rate of a Christmas Tree Fire
> 
> 
> 
> http://fire.nist.gov/bfrlpubs/fire08/PDF/f08014.pdf
> 
> 
> 
> I have learned that where I have imagined Big Dry Christmas Trees they were
> more like Medium Size Half Wet Scotch Pines...
> 
> 
> 
> 
> 