"These trees burned easily when ignited with a small open flame. Peak heat
release rates ranged from about 1.6 MW to 5.2 MW [6]. These heat release
rates for dry
trees were significantly higher than heat release rates for "Christmas"
trees that had been
published prior to that time [4,7]."

About 8 years ago I started pestering the P.E.'s here about their fire
modeling of required exhaust rates for smoke exhaust systems for atriums
from NFPA 92B. They used a 5MW HRR for smoke production. "That's 10 big dry
Christmas trees!" they would exclaim. Due to my recent spouting off about
the antifreeze final report I thought I had better see for myself. I
followed the above reference and sure enough, when they started doing it the
HRR for a "Christmas" tree was 500 kW. Of course it really does not matter
how many or big trees we imagine, I just like to paint a picture for myself
if I can. I think i'll stick to how may 100 watt light bulbs, as if they
were 100% efficient, (but not greater than) :)

And yes, it is very good to see that residential sprinklers can catch
extremely fast fires like they do.

brad

-----Original Message-----
From: Roland Huggins [mailto:[email protected]] 
Sent: Friday, January 31, 2014 11:15 AM
To: [email protected]
Subject: Re: Interesting reading-- Res Heads and Christmas Trees

Just glanced at the report.  According to the abstract, it self extinguishes
if the tree is not allowed to dry and and maintains a moisture content in
the needles in excess of 100%.  How does one exceed 100%?

The fire size for a dry tree was 3.2MW to 4.3MW with the needles consumed
within 60 seconds.  I remember the tree I fired-up in the backyard as a kid
went off like gasoline and gone in like 30 seconds.  Nonetheless, the fire
size for most of us would be much bigger cause the study used a fairly small
tree about 6 ft tall.

Good to see that a residential sprinkler contained such an aggressive fire.

 
Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Jan 31, 2014, at 7:14 AM, Brad Casterline <[email protected]>
wrote:

> Impact of a Residential Sprinkler on the
> 
> Heat Release Rate of a Christmas Tree Fire
> 
> 
> 
> http://fire.nist.gov/bfrlpubs/fire08/PDF/f08014.pdf
> 
> 
> 
> I have learned that where I have imagined Big Dry Christmas Trees they
were
> more like Medium Size Half Wet Scotch Pines...
> 
> 
> 
> 
> 
> Brad Casterline, NICET IV
> 
> Fire Protection Division
> 
> 
> 
> FSC, Inc.
> 
> P: 913-722-3473
> 
> [email protected]
> 
> www.fsc-inc.com
> 
> 
> 
> Engineering Solutions for the Built Environment
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to