I'm with Ben and don't like it, but if the rules are followed then using it for other than holding water would mean you've changed the configuration from an accepted omission to something else (like removing insulation that allowed you to omit sprinklers under a platform) thereby requiring a re-evaluation of the space. That should elicit a storm of postings from the what if crowd: "What if they don't fix it?" That's exactly the same as: "What if they drain it?" We can't work in what-ifs, because it's a badger hole. Not only is it deep and seemingly endless, but if you do get to the last what if you get mauled by the badger. No thanks. If the committee rules that omission is acceptable then I will omit per code. If it becomes storage for 100,000 yoga mats or 50 drums of methyl ethyl death then it needs changing to accommodate, not prior anticipation.
On Mon, Feb 3, 2014 at 3:48 PM, Ben Young <[email protected]> wrote: > Boo! > > > Benjamin Young > > > On Mon, Feb 3, 2014 at 6:47 PM, Roland Huggins > <[email protected]>wrote: > > > A very belated follow-up on this thread, the first draft will allow > > omission of sprinklers directly above the pool. Did not see anything on > > what about those cases where the pool drained and converted to storage. > > > > Roland > > > > > > Roland Huggins, PE - VP Engineering > > American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives > > Dallas, TX > > http://www.firesprinkler.org > > > > > > > > > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) A problem well stated is a problem half solved. -Charles F. Kettering, inventor and engineer (1876-1958) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org