I have sprinklers in combustible concealed spaces as required but NOT in the
combustible concealed spaces per 8.15.1.2.5 (where solid 2x10 wood joist
have fire rated ceilings directly attached). My question is does the 3,000
sqft minimum design area apply is this scenario? My confusion comes from
11.2.3.1.4 (3) and (4).

 

 

Will Crisler

Southeastern Automatic Sprinkler Co., Inc.

143 Enterprise Dr

P.O.  Box 1338

Madison, MS 39130-1338

Ph (601) 898-9385

Fx (601) 898-8230

(800)-898-0238

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to