I have sprinklers in combustible concealed spaces as required but NOT in the combustible concealed spaces per 8.15.1.2.5 (where solid 2x10 wood joist have fire rated ceilings directly attached). My question is does the 3,000 sqft minimum design area apply is this scenario? My confusion comes from 11.2.3.1.4 (3) and (4).
Will Crisler Southeastern Automatic Sprinkler Co., Inc. 143 Enterprise Dr P.O. Box 1338 Madison, MS 39130-1338 Ph (601) 898-9385 Fx (601) 898-8230 (800)-898-0238 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
