Subject: RE: 3,000 sq ft minimum design area rule...

It is not required for 3000 sf area calc.  See item 4 (d) under 11.2.3.1.4. 

Art Tiroly
ATCO Fire Protection

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Will 
Crisler
Sent: Wednesday, February 05, 2014 3:20 PM
To: [email protected]
Subject: 3,000 sq ft minimum design area rule...

I have sprinklers in combustible concealed spaces as required but NOT in the 
combustible concealed spaces per 8.15.1.2.5 (where solid 2x10 wood joist have 
fire rated ceilings directly attached). My question is does the 3,000 sqft 
minimum design area apply is this scenario? My confusion comes from
11.2.3.1.4 (3) and (4).

 

 