2009 IFC

312.1 General. Vehicle impact protection required by this
code shall be provided by posts that comply with Section 312.2
or by other approved physical barriers that comply with Section 312.3.

312.2 Posts. Guard posts shall comply with all of the following
requirements:
1. Constructed of steel not less than 4 inches (102 mm) in
diameter and concrete filled.
2. Spaced not more than 4 feet (1219 mm) between posts on
center.
3. Set not less than 3 feet (914 mm) deep in a concrete footing
of not less than a 15-inch (381 mm) diameter.
4. Set with the top of the posts not less than 3 feet (914 mm)
above ground.
5. Located not less than 3 feet (914 mm) from the protected
object.

312.3 Other barriers. Physical barriers shall be a minimum of
36 inches (914 mm) in height and shall resist a force of 12,000
pounds (53 375 N) applied 36 inches (914 mm) above the adjacent
ground surface.

Hope that helps,


John Drucker, CET
Assistant Construction Official
Fire Protection Subcode Official
Building/Fire/Electrical Inspector
Borough of Red Bank
Red Bank, New Jersey
Email: [email protected]
Cell/Text: 732-904-6823


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Owen
Evans
Sent: Saturday, February 8, 2014 7:32 PM
To: [email protected]
Subject: Bollard Diameter

Hello Folks,


The minimum diameter of a bollard protecting an FDC is 4" correct? Can
someone give me the code reference? 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to