Hi Bob,
You need 7 psi as a minimum (gauge pressure, dude...) on Double- and 
Non-Interlock systems. (you are counting on the sprinkler activation before the 
valve will operate, thus minimum 7 psi on the head itself...)
You have to supervise the piping on systems more than 20 sprinklers.  
Supervisory air is sometimes only ounces, but as you may already see, that 
would only be on a single interlock system.
Hope this is helpful info.
It should be recognized that the above is my opinion as a member of the NFPA, 
and has not been processed as a formal interpretation in accordance with the 
NFPA Regulations Governing Committee Projects and should therefore not be 
considered, nor relied upon, as the official position of the the NFPA, nor any 
of their technical committees. 

Sincerely,


Cecil Bilbo 
Academy of Fire Sprinkler Technology
Champaign, IL
217.607.0325
www.sprinkleracademy.com

[email protected]

 

OUR STUDENTS SAVE LIVES!!



> From: [email protected]
> To: [email protected]
> Subject: Small Pre-action System
> Date: Wed, 12 Feb 2014 16:50:36 -0700
> 
> It's been years since I have designed a small (3 sprinklers) single
> interlock pre-action system.  I have a vague remembrance of not needing an
> air supply for a system this small, but I can find that info anywhere.  I'm
> wondering if I'm confusing it with the requirement for supervision on
> systems over 20 sprinklers?  Or, is this where the 7 psi limitation comes
> in?  Atmospheric pressure is something like 14.7 psi so the 7 psi limit is
> meet?  
> 
> Dazed and confused in Idaho,
> 
> Thank you,
> 
> Bob Knight, CET III
> 208-318-3057
> www.firebyknight.com
> 
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
                                          
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to