Only if adopted Duane. Steve lives in IBC Land.

On Fri, Feb 21, 2014 at 3:51 AM, Johnson, Duane (NIH/OD/ORS) [C] <
[email protected]> wrote:

> 3.3.2 Bathroom.   Within a dwelling unit, any room or compartment
> dedicated to personal hygiene, containing a toilet, sink, or bathing
> capability such as a shower or tub.
>
> A.3.3.2 Bathroom.   A room is still considered a bathroom if it contains
> just a toilet. Additionally, two bathrooms can be adjacent to each other
> and are considered separate rooms, provided they are enclosed with the
> required level of construction. A compartment containing only a toilet,
> regardless of its intended use, is considered a bathroom.
>
> An interesting note...the existing hotel/dorm chapter 29 of NFPA 101
> (2013) has an exception for not installing sprinklers in bathrooms...
> 29.3.5.5    In guest rooms and in guest room suites, sprinkler
> installations shall not be required in closets not exceeding 24 ft2 (2.2
> m2) and in bathrooms not exceeding 55 ft2 (5.1 m2).
>
> However, this exception does not exist for new hotel/dorms chapter 28 of
> NFPA 101. Interpret this as you may. Also, NFPA 101 (the code), supersedes
> NFPA 13 (the standard).
>
>
> Duane Johnson, PE
> Program Manager
> Division of the Fire Marshal (Contractor)
> Office of Research Services
> National Institutes of Health
> 301-496-0487
>
> "Protecting Science - One Sprinkler at a Time"
>
>
> -----Original Message-----
> From: Steve Leyton [mailto:[email protected]]
> Sent: Thursday, February 20, 2014 7:40 PM
> To: [email protected]
> Subject: Bathroom/powder room/toilet room
>
> 2013 edition of 13 now requires sprinklers in all bathrooms except
> conforming small ones in hotels.   Anyone have insight on whether the
> toilet-only compartment of a larger bathroom is considered a "bathroom"
> or could that be excepted.  How about a powder room that has no cabinets
> or tub/shower but does have a basin and a toilet?
>
>
>
> Steve Leyton
>
> PROTECTION DESIGN & CONSULTING
>
> 2851 Camino del Rio South, Suite 400
>
> San Diego, CA 92108
>
> -------------------------------------------------------------
>
> Ph:      858.751.2930 - ext. 102
>
> Fax:    858.751.2933
>
> Cell:  619.972.5696
>
>
>
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to