yep

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve 
Leyton
Sent: Wednesday, February 26, 2014 11:31 AM
To: [email protected]
Subject: RE: NFPA 14 7.10.1.1.3 (2013)

Is it all one big ST system with the building risers fed by a common supply in 
the podium?


SL

-------- Original message --------
From: [email protected] 
Date:02/26/2014  9:48 AM  (GMT-08:00) 
To: [email protected] 
Subject: NFPA 14 7.10.1.1.3 (2013) 

We have 4 buildngs each less than 80k sqft on a level but they sit on top of a 
100k sqft garage. Do we calc 500, 500 in the towers or 500, 250 and pick up 
another 250 in the garage to get 1000 max?
Ron F