but do you get to 1000 via 1)500+500 or 2)500+250+250?

-----Original Message-----
From: Steve Leyton [mailto:[email protected]] 
Sent: Wednesday, February 26, 2014 12:55 PM
To: [email protected]
Subject: RE: NFPA 14 7.10.1.1.3 (2013)

Then it would be 1000 gpm overall (assuming fully spkrd environment) using
the hydraulically most remote 3 standpipes. Sez me.

The preceding is my opinion only.

SL

-------- Original message --------
From: [email protected] 
Date:02/26/2014  10:31 AM  (GMT-08:00) 
To: [email protected] 
Subject: RE: NFPA 14 7.10.1.1.3 (2013) 

yep

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Leyton
Sent: Wednesday, February 26, 2014 11:31 AM
To: [email protected]
Subject: RE: NFPA 14 7.10.1.1.3 (2013)

Is it all one big ST system with the building risers fed by a common supply
in the podium?


SL

-------- Original message --------
From: [email protected] 
Date:02/26/2014  9:48 AM  (GMT-08:00) 
To: [email protected] 
Subject: NFPA 14 7.10.1.1.3 (2013) 

We have 4 buildngs each less than 80k sqft on a level but they sit on top of
a 100k sqft garage. Do we calc 500, 500 in the towers or 500, 250 and pick
up another 250 in the garage to get 1000 max?
Ron F

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to