100% guess, but the first two may be intended to support the fire sprinkler 
system in the building with the third one coming on late in a bad game to 
support hose streams.

Just a thought.

J. Scott Mitchell, PE


Sent from my Verizon Wireless 4G LTE smartphone

-------- Original message --------
From: Brad Casterline <[email protected]> 
Date:03/06/2014  8:14 PM  (GMT-06:00) 
To: [email protected] 
Subject: Re: Pump House Controls 

Correction on pump #3? Should be 2500 @ 65, not 2000 @ 65?

> On Mar 6, 2014, at 6:54 PM, "Tom Duross" <[email protected]> wrote:
> 
> I have a question regarding how you guys would control this.
> 
> Outside pump house with aboveground tank, 500,000 gal.
> Three diesel drive fire pumps in parallel from 10" tank supply to 10" yard
> supply.
> All three pumps are rated at 2500 GPM but different pressure ratings.
> I have no design information right now but it's a record storage facility,
> 50' high piles of paper, fwiw.
> I'm looking at replacing one of the pumps, the oldest and original, I'll
> call it pump #1.
> Pump #1, original 1971 is a 10x8 rated for 2500@125 PSI.
> Pump #2 was replaced in 2003, same model 10x8, nice tier 2, 2500@125.
> Check.
> Pump #3 was replaced in 1994, same model 10x8, but 2000@65.  Huh?
> Jockeys are dual vertical turbine, 100@140.  Check.
> If I work under the premise of direct replacement and quote a 2500@125, tier
> 3 or 4,
> how would you guys balance these pumps for lead to lag with a pump so small
> compared to the rest?
> Pump #2 becomes the lead pump and #1 and #3 fall in 10# each behind?
> TD
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to