Hello Todd,

There might have been an office area in there at one time the smaller pump was 
for. No telling from here :) Good Luck and please let us know what you end up 
doing.

Friday, March 7, 2014, 2:23:27 PM, you wrote:

> I have no idea what the purpose of the smaller pump is. The
> 2500@125 pump would (in theory) produce 3750 gpm at 81 psi. The
> churn pressure for the 2000@65 pump is 78 psi. The smaller pump is
> not going to have any impact on the available water until the
> pressure falls below 78 psi, which would probably be somewhere
> around 4000 gpm (assuming the actual flow will exceed the 150%
> point). If all 3 pumps are flowing, that number goes up to 8000 gpm.
> At 8000 gpm, 500000 gallons will last 62.5 minutes. If you have a
> fire that is demanding 8000 gpm, it is probably time to get out the 
> marshmallows and call CNN.

> I know there were some funky things that went on with the old IRI
> Maximum Reliability Systems. Could this have possible been one of those?

> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> www.fpdc.com
> 860-535-2080 (ofc)

> Begin forwarded message:

>> From: Todd - Work <[email protected]>
>> Date: February 25, 2014 at 4:42:15 PM EST
>> To: Barbara Corbeil <[email protected]>
>> Subject: Video by uconnwbb
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> www.fpdc.com
> 860-535-2080 (ofc)

>> On Mar 7, 2014, at 7:57 AM, "Tom Duross" <[email protected]> wrote:

>> I emailed and received order info on the remaining original pump.  I emailed
>> the factory back and asked if three were ordered at once and what the sizes
>> were.
>> I have no idea what the demand is Todd, maybe I should refer you to take a
>> look on that end.  I do know it was a refrigerated warehouse when the order
>> was placed in 1971.
>> I just boggles me that, assuming they were all the same, one replacement was
>> ordered so small.  Two 2500@125 and one 2000@65.  Not even 2000@125,
>> 2000@65.
>> Scott, my thinking (and it's just me) would be to progress from small to
>> large like with jockeys when in duplex/triplex fashion.
>> The automatic pressure controls will be difficult either way so maybe sync
>> the baby for lag 2 seeing yard pressures will probably be down 75-100 PSI at
>> that point.
>> I doesn't appear much has been done here in 10 years and it's an FM job
>> which is surprising.
>> I do have some thoughts about PLD and possibly a lower pressure on the
>> replacement for the remaining original but can't make a move until someone
>> smarter than me looks at what's on the other end of that 150 PSI yard main
>> and huge building full of paper.
>> I've also reached out to the local shop who replaced 2 of them but not
>> getting much response.
>> I'll keep the list updated.
>> TD

>> I'll ask another question. How many and what size pumps are required to meet
>> the sprinkler demand?

>> Todd G Williams, PE

>>>> On Mar 6, 2014, at 10:08 PM, Brad Casterline <[email protected]>
>>> wrote:

>>> It occurs to me you are looking for answers not questions-- I'll run 
>>> back up to the nosebleed section now and just spectate

>>>> On Mar 6, 2014, at 8:41 PM, Brad Casterline <[email protected]>
>> wrote:

>>>> Shouldn't the order of operation be farthest from tank, middle, closest
>> to tank? Especially if farthest is weakest?

>>>>> On Mar 6, 2014, at 8:30 PM, "J. Scott Mitchell, PE"
>> <[email protected]> wrote:

>>>>> 100% guess, but the first two may be intended to support the fire
>> sprinkler system in the building with the third one coming on late in a bad
>> game to support hose streams.

>>>>> Just a thought.

>>>>> J. Scott Mitchell, PE


>>>>> Sent from my Verizon Wireless 4G LTE smartphone


>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



-- 
Best regards,
Charles Thurston                          mailto:[email protected]
Systems Design Manager
NICET Certified

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to