Depends on whether it is an NFPA 13 job or an FM job.  NFPA does not say but FM 
calls the top of the flutes as the ceiling if they are wide enough between 
flutes.  Don't recall the width offhand but think if 6 inches wide then you use 
the top of the flutes.

John Hoffman

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of G. Tim 
Stone
Sent: Thursday, March 13, 2014 1:32 PM
To: [email protected]
Subject: Warehouse Ceiling Question?

What is the Ceiling in a Warehouse?

 

Scenario:

Packaged Steel Frame Building. Red iron frames spaced 30' between. 12" steel Z 
shaped purlins, spaced 3'-7" on center on top of the Red Iron frames.
Steel Q-Deck pan (about 3.5" - 4" deep) attached to top of the Z purlins.

High point of the building is 30'-0" AFF, ΒΌ : 12 roof pitch.  The building 
insulation is on top of the Q-Deck. No vinyl insulated blanket that we usually 
see in warehouse construction.

 

The occupancy is Group A Plastics, High Piled and rack storage, Storage height 
to 17'-0 AFF, ESFR Pendent Sprinklers, Depending on Manufacture used, 
deflectors can be up to 18" down below "CEILING".

 

Is the "CEILING" at the point where the Q-Deck that rests on top of the purlin 
or is it the top of the pocket formed in the Q-Deck? I will rephrase, Is the 
"CEILING" at the top of the purlin or 3.5" - 4" higher (high point of 
Q-Decking)?

 

Thank you in advance for clarification.

 

Regards,

G. Tim Stone

 

G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services

 

                117 Old Stage Rd. - Essex Jct., VT. 05452

CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343

                           [email protected]

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to