I am not seeing anything in NFPA 13 that says this.  Maybe just missing it, but 
the definition of ceiling height (2013 edition) is 3.3.3. and  just mentions 
"to the underside of the ceiling or roof deck".

If you look at one mfrs spec sheet for k25 ESFR here is what it says.

NFPA 13 Deflector-to-Ceiling
Distance
6 to 18 inches (152 to 457 mm)
FM 2-0
Consult FM and/or FM Guidelines for allowable deflector-to-ceiling distances as 
well as thermal sensing element-to-ceiling criteria.

Note that FM uses the centerline of the thermal sensing element and NOT the 
deflector.  Plus they talk about (somewhere) the width, and maybe the height of 
the metal deck pockets and give criteria of where to measure from - top or 
bottom.

John Hoffman

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bob
Sent: Thursday, March 13, 2014 1:40 PM
To: [email protected]
Subject: RE: Warehouse Ceiling Question?

I think 13 addresses this with 3" and less deep the bottom is the deck, if 
greater  than 3" than the upper part of the channel is the deck.  Sorry I don't 
have time to look up code, but you might want to check my numbers.

Thank You,

Bob Knight, CET III
208-318-3057
www.Firebyknight.com



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of G. Tim 
Stone
Sent: Thursday, March 13, 2014 12:32 PM
To: [email protected]
Subject: Warehouse Ceiling Question?

What is the Ceiling in a Warehouse?

 

Scenario:

Packaged Steel Frame Building. Red iron frames spaced 30' between. 12" steel Z 
shaped purlins, spaced 3'-7" on center on top of the Red Iron frames.
Steel Q-Deck pan (about 3.5" - 4" deep) attached to top of the Z purlins.

High point of the building is 30'-0" AFF, ΒΌ : 12 roof pitch.  The building 
insulation is on top of the Q-Deck. No vinyl insulated blanket that we usually 
see in warehouse construction.

 

The occupancy is Group A Plastics, High Piled and rack storage, Storage height 
to 17'-0 AFF, ESFR Pendent Sprinklers, Depending on Manufacture used, 
deflectors can be up to 18" down below "CEILING".

 

Is the "CEILING" at the point where the Q-Deck that rests on top of the purlin 
or is it the top of the pocket formed in the Q-Deck? I will rephrase, Is the 
"CEILING" at the top of the purlin or 3.5" - 4" higher (high point of 
Q-Decking)?

 

Thank you in advance for clarification.

 

Regards,

G. Tim Stone

 

G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services

 

                117 Old Stage Rd. - Essex Jct., VT. 05452

CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343

                           [email protected]

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to