Good morning to all of you. I have a project for a roll paper storage in a warehouse with 44' height. The FM Global design is 20 K16.8 @ 50 psi + 500 gpm by 120 minutes. The fire pump is 2,500 gpm @ 125 psi and the water tank for 269,924 gals. The preliminary calculations give me 2,130 gals @ 145 psi at the BOR. The pump room and tank is about 900 ft. from the BOR and have 8" PVP pipe. The grid system is: 8" primary main, 4" secondary main, 2.5" branch lines. The sprinkler head are pendent connected through arm-over of 1.5" pipe.
The issue here is that the distance and Pipe size from the BOR and Pump give a lot of pressure and velocity. What do you recommend to work around? Booster pump near the BOR? Regards! ________________________________ This year we are focused on improving our service ... Your feedback is extremely helpful. Feel free to support us. Have a safe day! Ing Gerzayn Fuentes Campos | Director CEPI Specialist in Fire Projects. Tel +52 (81) 1766-0800 x 106 | http://www.cepi.mx Regia Vista # 500 | Linda Vista | Guadalupe | Nuevo Leon | Mexico | 67130 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org