Right Brad,

That's my assumption.  You plug in some pipe sizes and pump data, minimum end 
head pressure desired and run the calc.  There are times when what comes out 
the first pass is not within the required range so you tweak sizes until you 
can get it to work.

He didn't state that but it's my best guess.  We don't know what is new or 
existing, if there is any opportunity to make any changes or what.  

Fire flow isn't mentioned as that is what really drives the tank and pump in 
most cases but the project location may make that a non-issue.  

Yes volume of tank is an odd number.  

Quick numbers, I'm figuring actual flow with hose is closer to 3200 gpm (+/-) X 
120 minutes, tank should be more like 390K to 400K gallons.

Craig L. Prahl, CET   
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Brad 
Casterline
Sent: Tuesday, March 18, 2014 4:26 PM
To: [email protected]
Subject: RE: 20 K16.8 @ 50 + 500 x 120mins

I see Craig, like a supply calc and that is all Gerzayn can get.
No matter what pipe diam and location of the pump, the tank will have to be 
bigger I think because 2376*120=285,120 Gal. That's with no overage or hose!

Brad

-----Original Message-----
From: [email protected] [mailto:[email protected]]
Sent: Tuesday, March 18, 2014 1:28 PM
To: [email protected]
Subject: RE: 20 K16.8 @ 50 + 500 x 120mins

My assumption was that due to design issues, he's coming up short.  

Craig L. Prahl



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad 
Casterline
Sent: Tuesday, March 18, 2014 2:09 PM
To: [email protected]
Subject: RE: 20 K16.8 @ 50 + 500 x 120mins

Something else to think about Gerzayn:

Q=k*p^.5= 16.8*7.071=118.794*(20) heads=2376 GPM minimum. How did you get
2130 demand at BOR?

Brad

-----Original Message-----
From: [email protected] [mailto:[email protected]]
Sent: Tuesday, March 18, 2014 12:55 PM
To: [email protected]
Subject: RE: 20 K16.8 @ 50 + 500 x 120mins

Sounds like you will be trying some different pipe sizes on the sprinkler
system. 8" and 4" is a pretty wide spread on the mains.    I'd look at
pressure losses in the aboveground system and see if you can improve on those.

As far as the underground, I'm assuming you are using a plastic pipe (PVP), and 
from a quick calculation (2,200 gpm) it looks like a velocity of around
16-17 feet per second with a pressure drop around 23-25+ psi for the 900 ft 
length not taking into consideration fittings.  

Don't worry too much about the velocity if you're dealing with closed head 
systems.  

If you can change the underground to 10" it would be of great benefit to the 
whole design.  One thing that is often overlooked with regard to underground 
pipe sizes is that fire fighting and suppression is done by manual hose line, 
not from sprinklers.  So the more water available to hydrants, the better.  The 
pump can run up to 3,750 gpm which in an 8" pipe really generates some 
considerable friction loss.  



Craig L. Prahl



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Gerzayn 
Fuentes @ CEPI.MX
Sent: Tuesday, March 18, 2014 12:51 PM
To: [email protected]
Subject: 20 K16.8 @ 50 + 500 x 120mins

Good morning to all of you.
I have a project for a roll paper storage in a warehouse with 44' height.
The FM Global design is 20 K16.8 @ 50 psi + 500 gpm by 120 minutes.
The fire pump is 2,500 gpm @ 125 psi and the water tank for 269,924 gals.
The preliminary calculations give me 2,130 gals @ 145 psi at the BOR.
The pump room and tank is about 900 ft. from the BOR and have 8" PVP pipe.
The grid system is: 8" primary main, 4" secondary main, 2.5" branch lines.
The sprinkler head are pendent connected through arm-over of 1.5" pipe.

The issue here is that the distance and Pipe size from the BOR and Pump give a 
lot of pressure and velocity.

What do you recommend to work around?
Booster pump near the BOR?

Regards!

________________________________
This year we are focused on improving our service ... Your feedback is 
extremely helpful. Feel free to support us.
Have a safe day!

Ing Gerzayn Fuentes Campos | Director
CEPI Specialist in Fire Projects.
Tel +52 (81) 1766-0800 x 106 | http://www.cepi.mx

Regia Vista # 500  | Linda Vista |  Guadalupe  | Nuevo Leon |  Mexico  |
67130 _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________