fill the space w/ non-comb insulation :)

-----Original Message-----
From: Travis Mack [mailto:[email protected]] 
Sent: Wednesday, March 19, 2014 2:04 PM
To: [email protected]
Subject: BIA and concealed spaces

We are looking at a project with the BIA (Bureau of Indian Affairs).  
They require all bldgs over 2000 sq ft to be Ord Grp I as a minimum in 
ALL areas.  We have dealt with them in the past and there seems to be no 
waivering on this issue.  We had a contractor in the past install Tyco 
BB heads and calc'd for 0.15 gpm.  Tyco had written letters that 
calculating to 0.15 would be fine. But the data sheet for those heads 
says light hazard.  So, the BIA rejected and the attic had to be 
re-piped for SSU for protection.

Now, the current project has concealed combustible spaces requiring the 
specially listed heads for flat, shallow concealed combustible spaces - 
Tyco CC, Viking COIN, etc..  However, we are going to have the problem 
that these heads are listed for light hazard only.  We can't go to SSU 
because NFPA 13 states that you must use specially listed heads for 
these concealed spaces.  We are awaiting a response from the BIA, but I 
am not expecting much help.  Have any of you ever run into this?  If so, 
how did you address it?  We can't use the only heads listed for the area 
because they are only listed as light hazard and the BIA requires all 
areas to be OH1 minimum.  We can't use SSU sprinklers because NFPA 13 
prohibits their use in these spaces.  It is a true Catch 22.

-- 
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to