Do you really need to have the standard spray uprights specifically listed for the combustible concealed space? If you look at NFPA 13 2007 8.4.1.1 it says "Upright and pendent spray sprinklers shall be permitted in all occupancy hazard classifications and building construction types." I know what section your referring to about specifically listed for combustible concealed spaces ( I cannot for the life of me find it right now). I was always under the interpretation that this specific section would allow you to use specifically listed sprinkler heads if you couldn't comply with table 8.6.2.2.1 (a)
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Travis Mack Sent: Wednesday, March 19, 2014 3:04 PM To: [email protected] Subject: BIA and concealed spaces We are looking at a project with the BIA (Bureau of Indian Affairs). They require all bldgs over 2000 sq ft to be Ord Grp I as a minimum in ALL areas. We have dealt with them in the past and there seems to be no waivering on this issue. We had a contractor in the past install Tyco BB heads and calc'd for 0.15 gpm. Tyco had written letters that calculating to 0.15 would be fine. But the data sheet for those heads says light hazard. So, the BIA rejected and the attic had to be re-piped for SSU for protection. Now, the current project has concealed combustible spaces requiring the specially listed heads for flat, shallow concealed combustible spaces - Tyco CC, Viking COIN, etc.. However, we are going to have the problem that these heads are listed for light hazard only. We can't go to SSU because NFPA 13 states that you must use specially listed heads for these concealed spaces. We are awaiting a response from the BIA, but I am not expecting much help. Have any of you ever run into this? If so, how did you address it? We can't use the only heads listed for the area because they are only listed as light hazard and the BIA requires all areas to be OH1 minimum. We can't use SSU sprinklers because NFPA 13 prohibits their use in these spaces. It is a true Catch 22. -- Travis Mack, SET MFP Design, LLC 2508 E Lodgepole Drive Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:[email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ______________________________________________________________________ This email has been scanned by the Symantec Email Security.cloud service. For more information please visit http://www.symanteccloud.com ______________________________________________________________________ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org