One is an occupied floor area.  The other is an obstruction between the ceiling 
sprinkler and the floor area.

Also worth noting that the identified section has been changed.  It was 
appropriate when ESFR sprinklers added the additional sprinkler(s) below 
obstructions.  Since that is no longer true case, it’s sprinklers in general.

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Mar 20, 2014, at 7:23 AM, [email protected] wrote:

> Gentlemen,
> 
> NFPA 13 par. 23.4.4.6.3 states:
> The requirements of 23.4.4.6.1.1 to include every
> sprinkler in the design area shall not apply where spray sprin-
> klers or CMSA sprinklers are provided above and below ob-
> structions such as wide ducts or tables.
> 
> Question:
> Does the same apply to sprinklers underneath mezzanines?
> 
> And how about sprinklers under a floor with a large opening to the 
> (sprinklered) floor above?
> 
> And how when the large opening is filled with obstructions (pipe rack) with 
> additional sprinklers underneath the obstructions?
> 
> Looking forward to your insight....
> 
> 
> Best regards,
> 
> Frans Stoop
> TOS architecture & fire protection
> Netherlands <[email protected]>