And how is this your problem Rod? If you must write a letter saying in your
expert opinion this won't work and sprinklers should be added. Give a
contingency number for an attic dry if you're in the bidding phase. Unless
you're an insulation contractor bidding that, as well as the sprinkler guy,
and bidding that, it's not your problem. Let the architect, the GC, and the
insulator sort it all out. I believe the "fill the void space with
non-combustible insulation" concept was for smaller spaces like under
platforms, small concealed spaces, etc., not whole building, peaked attic
spaces. Of course it doesn't restrict the size, so I'm probably wrong. I'll
let the Hugginses and Druckerses weigh in on intent.

Smeagal Greenman


On Mon, Mar 24, 2014 at 2:24 PM, John Drucker - Home <
[email protected]> wrote:

> Rod,
>
> I experienced this exact situation.  In order to blow it in the drywall has
> to be in place on the underside with installation holes bored in the
> decking
> above.  The holes (typically 2") have to be properly placed and spaced and
> are left open after installation for inspection where a stick is used to
> determine if there are any voids.  Where a void exists the stick will cause
> the insulation level to drop requiring it to be topped off. It's a ton of
> work to avoid putting sprinklers in a qualified concealed space.
>
> PS, If they ever ever open the ceiling, oh boy, like an hour glass it pours
> out requiring reinstallation of semi rigid insulation such as roxul or
> thermafiber.
>
> I have pics if you want to see, off list.
>
>
> John Drucker, CET
> Assistant Construction Official
> Fire Protection Subcode Official
> Building/Fire/Electrical Inspector
> Borough of Red Bank
> Red Bank, New Jersey
> Email: [email protected]
> Cell/Text: 732-904-6823
>
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Rod
> DiBona
> Sent: Monday, March 24, 2014 4:59 PM
> To: [email protected]
> Subject: truss filled with insulation
>
>
>
> I have an apartment building where the architect took the area increases
> for
> a full 13 system. They are utilizing a 16"open web truss in between the
> floors. The mechanical is running hvac in the truss. The sections show the
> space filled with insulation with an accompanying note that states that it
> will be. My question is how is this "completely filled with non -
> combustible insulation?" They are planning on blowing in the insulation
> around all the duct etc that is in the space but it just seems really hard
> to believe that it will indeed be completely filled. I remember a while
> back
> Roland tried to get a 2" gap on the top and I think that was a battle. I am
> picturing the duct blocking insulation from getting in plenty of spots.
> Maybe not? Any thougts?
>
> Rod at Rapid
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to