Charles did that in a Buddhist temple with a pagoda style roof, so multiple
eaves at every level. If I recall it was three sets of eaves for each of
three floors and then five for the roof. The attic was a piece of cake
after filling the eaves with batts, lots of cheap helper monk labor, and
then rocking them off for eternity. The Abbot was a fun guy that could
barely speak English. If you've never seen me I'm bald and have big ears,
which fascinated him.


On Mon, Mar 24, 2014 at 6:48 PM, John Drucker - Home <
[email protected]> wrote:

> 2013 NFPA-13
>
> 8.15.1 Concealed Spaces.
> 8.15.1.1 Concealed Spaces Requiring Sprinkler Protection.
> Concealed spaces of exposed combustible construction shall
> be protected by sprinklers except in concealed spaces where
> sprinklers are not required to be installed by 8.15.1.2.1
> through 8.15.1.2.18 and 8.15.6.
>
> 8.15.1.2.7 Concealed spaces filled with noncombustible insulation
> shall not require sprinkler protection.
>
> PS, heres Rolands, 2" air gap.........(change for the 2013 Edition)
>
> 8.15.1.2.7.1 A maximum 2 in. (50 mm) air gap at the top of
> the space shall be permitted.
>
>
> John Drucker, CET
> Fire Protection Subcode Official
> Fire / Building / Electrical Inspector
> New Jersey
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> Charles
> Thurston
> Sent: Monday, March 24, 2014 9:36 PM
> To: [email protected]
> Subject: Re: truss filled with insulation
>
> Hello
>
> Speaking of concealed spaces. I have a project where the water pressure is
> marginal. BB heads will cover the span and there is enough pressure for
> them
> to work properly. The problem is there are 2 areas where the building gets
> about 4 feet wider on each side. BB will not cover, Need coin for the eves
> in these areas. IF they wall those areas off with sheetrock on the outside
> and fill them with insulation. Is that now a concealed space that does not
> have to be sprinkled?
>
> Monday, March 24, 2014, 8:11:58 PM, you wrote:
>
> > Very interesting. Not the detection method I would have thought of but
> effective!
>
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of
> > [email protected]
> > Sent: Monday, March 24, 2014 5:53 PM
> > To: [email protected]
> > Subject: Re: truss filled with insulation
>
> > More to my experience.....does the filling of combustible concealed space
> limit fire spread ?, Yes.
>
> > The building in question was a four (4) story pedestal 13R.  A couple
> > years back an electrical fire occurred in an improperly spliced
> > feeder.  The fire was contained to a an area of appx 2 cubic feet with
> > minor fire damage.  The interesting part was how it was detected, by
> > the failure of cpvc pipe that had eventually melted from the arcing
> > heat resulting in waterflow.  So yes properly filled concealed spaces
> > do limit fire spread.
>
> > John Drucker.
> > John Drucker
>
> > -----Original Message-----
> > From: Rod DiBona <[email protected]>
> > Sender: [email protected]
> > Date: Mon, 24 Mar 2014 23:15:23
> > To:
> > [email protected]<[email protected]
> > ler.org>
> > Reply-To: [email protected]
> > Subject: RE: truss filled with insulation
>
> > John,
>
> > Thank you for the input. Would love to see the pictures offline if you
> > get a chance. [email protected]
>
> > Ron - In this case we are proposing a different building type with
> > separation walls and a 13R system. Not only will it save the owner
> > money but we are an investor on the project. The savings side of the
> > cost benefit analysis is much greater for the 13R if the truss space
> > was to be sprinklered. Clear benefits to the full 13 but wanting to
> > know the true difference. Per John's email below looks like this can
> > be done but isn't easy. Just didn't seem right to me.
>
> > Thank you both as always.
>
> > Rod at Rapid
>
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of
> rongreenman .
> > Sent: Monday, March 24, 2014 5:00 PM
> > To: [email protected]
> > Subject: Re: truss filled with insulation
>
> > And how is this your problem Rod? If you must write a letter saying in
> > your expert opinion this won't work and sprinklers should be added.
> > Give a contingency number for an attic dry if you're in the bidding
> > phase. Unless you're an insulation contractor bidding that, as well as
> > the sprinkler guy, and bidding that, it's not your problem. Let the
> > architect, the GC, and the insulator sort it all out. I believe the
> > "fill the void space with non-combustible insulation" concept was for
> > smaller spaces like under platforms, small concealed spaces, etc., not
> > whole building, peaked attic spaces. Of course it doesn't restrict the
> > size, so I'm probably wrong. I'll let the Hugginses and Druckerses
> > weigh in on intent.
>
> > Smeagal Greenman
>
>
> > On Mon, Mar 24, 2014 at 2:24 PM, John Drucker - Home <
> [email protected]> wrote:
>
> >> Rod,
>
> >> I experienced this exact situation.  In order to blow it in the
> >> drywall has to be in place on the underside with installation holes
> >> bored in the decking above.  The holes (typically 2") have to be
> >> properly placed and spaced and are left open after installation for
> >> inspection where a stick is used to determine if there are any voids.
> >> Where a void exists the stick will cause the insulation level to drop
> >> requiring it to be topped off. It's a ton of work to avoid putting
> >> sprinklers in a qualified concealed space.
>
> >> PS, If they ever ever open the ceiling, oh boy, like an hour glass it
> >> pours out requiring reinstallation of semi rigid insulation such as
> >> roxul or thermafiber.
>
> >> I have pics if you want to see, off list.
>
>
> >> John Drucker, CET
> >> Assistant Construction Official
> >> Fire Protection Subcode Official
> >> Building/Fire/Electrical Inspector
> >> Borough of Red Bank
> >> Red Bank, New Jersey
> >> Email: [email protected]
> >> Cell/Text: 732-904-6823
>
>
>
>
> >> -----Original Message-----
> >> From: [email protected]
> >> [mailto:[email protected]] On Behalf Of
> >> Rod DiBona
> >> Sent: Monday, March 24, 2014 4:59 PM
> >> To: [email protected]
> >> Subject: truss filled with insulation
>
>
>
> >> I have an apartment building where the architect took the area
> >> increases for a full 13 system. They are utilizing a 16"open web
> >> truss in between the floors. The mechanical is running hvac in the
> truss.
> >> The sections show the space filled with insulation with an
> >> accompanying note that states that it will be. My question is how is
> >> this "completely filled with non - combustible insulation?" They are
> >> planning on blowing in the insulation around all the duct etc that is
> >> in the space but it just seems really hard to believe that it will
> >> indeed be completely filled. I remember a while back Roland tried to
> >> get a 2" gap on the top and I think that was a battle. I am picturing
> >> the duct blocking insulation from getting in plenty of spots.
> >> Maybe not? Any thougts?
>
> >> Rod at Rapid
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
>
> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
> >> l
> >> er.org
>
>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
>
> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
> >> l
> >> er.org
>
>
>
>
> > --
> > Ron Greenman
> > Instructor
> > Fire Protection Engineering Technology Bates Technical College
> > 1101 So. Yakima Ave.
> > Tacoma, WA 98405
>
> > [email protected]
>
> > http://www.bates.ctc.edu/fireprotection/
>
> > 253.680.7346
> > 253.576.9700 (cell)
>
> > Member:
> > ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>
> > They are happy men whose natures sort with their vocations.
> > -Francis Bacon, essayist, philosopher, and statesman (1561-1626)
>
> > A problem well stated is a problem half solved. -Charles F.
> > Kettering, inventor and engineer (1876-1958)
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
>
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
>
>
> > CONFIDENTIAL AND PROPRIETARY:
> > This email message is intended only for the use of the individual or
> > entity to which it is addressed and may contain information that is
> > privileged and confidential, nor is it, unless specifically stated,
> > intended to be relied upon by any person or persons other than the
> > individual or entity named above and no warranties or representations
> > are made or intended to persons or entities not named above.  If the
> > reader is not the intended recipient, you are hereby notified that any
> > dissemination, distribution or copying of this communication is
> > strictly prohibited.  If you have received this communication in
> > error, please notify us immediately by telephone, return this message
> > to the address above and delete all copies.  Thank you.
>
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
>
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
>
>
>
> --
> Best regards,
> Charles Thurston                          mailto:[email protected]
> Systems Design Manager
> NICET Certified
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to