Charles did that in a Buddhist temple with a pagoda style roof, so multiple eaves at every level. If I recall it was three sets of eaves for each of three floors and then five for the roof. The attic was a piece of cake after filling the eaves with batts, lots of cheap helper monk labor, and then rocking them off for eternity. The Abbot was a fun guy that could barely speak English. If you've never seen me I'm bald and have big ears, which fascinated him.
On Mon, Mar 24, 2014 at 6:48 PM, John Drucker - Home < [email protected]> wrote: > 2013 NFPA-13 > > 8.15.1 Concealed Spaces. > 8.15.1.1 Concealed Spaces Requiring Sprinkler Protection. > Concealed spaces of exposed combustible construction shall > be protected by sprinklers except in concealed spaces where > sprinklers are not required to be installed by 8.15.1.2.1 > through 8.15.1.2.18 and 8.15.6. > > 8.15.1.2.7 Concealed spaces filled with noncombustible insulation > shall not require sprinkler protection. > > PS, heres Rolands, 2" air gap.........(change for the 2013 Edition) > > 8.15.1.2.7.1 A maximum 2 in. (50 mm) air gap at the top of > the space shall be permitted. > > > John Drucker, CET > Fire Protection Subcode Official > Fire / Building / Electrical Inspector > New Jersey > > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of > Charles > Thurston > Sent: Monday, March 24, 2014 9:36 PM > To: [email protected] > Subject: Re: truss filled with insulation > > Hello > > Speaking of concealed spaces. I have a project where the water pressure is > marginal. BB heads will cover the span and there is enough pressure for > them > to work properly. The problem is there are 2 areas where the building gets > about 4 feet wider on each side. BB will not cover, Need coin for the eves > in these areas. IF they wall those areas off with sheetrock on the outside > and fill them with insulation. Is that now a concealed space that does not > have to be sprinkled? > > Monday, March 24, 2014, 8:11:58 PM, you wrote: > > > Very interesting. Not the detection method I would have thought of but > effective! > > > -----Original Message----- > > From: [email protected] > > [mailto:[email protected]] On Behalf Of > > [email protected] > > Sent: Monday, March 24, 2014 5:53 PM > > To: [email protected] > > Subject: Re: truss filled with insulation > > > More to my experience.....does the filling of combustible concealed space > limit fire spread ?, Yes. > > > The building in question was a four (4) story pedestal 13R. A couple > > years back an electrical fire occurred in an improperly spliced > > feeder. The fire was contained to a an area of appx 2 cubic feet with > > minor fire damage. The interesting part was how it was detected, by > > the failure of cpvc pipe that had eventually melted from the arcing > > heat resulting in waterflow. So yes properly filled concealed spaces > > do limit fire spread. > > > John Drucker. > > John Drucker > > > -----Original Message----- > > From: Rod DiBona <[email protected]> > > Sender: [email protected] > > Date: Mon, 24 Mar 2014 23:15:23 > > To: > > [email protected]<[email protected] > > ler.org> > > Reply-To: [email protected] > > Subject: RE: truss filled with insulation > > > John, > > > Thank you for the input. Would love to see the pictures offline if you > > get a chance. [email protected] > > > Ron - In this case we are proposing a different building type with > > separation walls and a 13R system. Not only will it save the owner > > money but we are an investor on the project. The savings side of the > > cost benefit analysis is much greater for the 13R if the truss space > > was to be sprinklered. Clear benefits to the full 13 but wanting to > > know the true difference. Per John's email below looks like this can > > be done but isn't easy. Just didn't seem right to me. > > > Thank you both as always. > > > Rod at Rapid > > > -----Original Message----- > > From: [email protected] > > [mailto:[email protected]] On Behalf Of > rongreenman . > > Sent: Monday, March 24, 2014 5:00 PM > > To: [email protected] > > Subject: Re: truss filled with insulation > > > And how is this your problem Rod? If you must write a letter saying in > > your expert opinion this won't work and sprinklers should be added. > > Give a contingency number for an attic dry if you're in the bidding > > phase. Unless you're an insulation contractor bidding that, as well as > > the sprinkler guy, and bidding that, it's not your problem. Let the > > architect, the GC, and the insulator sort it all out. I believe the > > "fill the void space with non-combustible insulation" concept was for > > smaller spaces like under platforms, small concealed spaces, etc., not > > whole building, peaked attic spaces. Of course it doesn't restrict the > > size, so I'm probably wrong. I'll let the Hugginses and Druckerses > > weigh in on intent. > > > Smeagal Greenman > > > > On Mon, Mar 24, 2014 at 2:24 PM, John Drucker - Home < > [email protected]> wrote: > > >> Rod, > > >> I experienced this exact situation. In order to blow it in the > >> drywall has to be in place on the underside with installation holes > >> bored in the decking above. The holes (typically 2") have to be > >> properly placed and spaced and are left open after installation for > >> inspection where a stick is used to determine if there are any voids. > >> Where a void exists the stick will cause the insulation level to drop > >> requiring it to be topped off. It's a ton of work to avoid putting > >> sprinklers in a qualified concealed space. > > >> PS, If they ever ever open the ceiling, oh boy, like an hour glass it > >> pours out requiring reinstallation of semi rigid insulation such as > >> roxul or thermafiber. > > >> I have pics if you want to see, off list. > > > >> John Drucker, CET > >> Assistant Construction Official > >> Fire Protection Subcode Official > >> Building/Fire/Electrical Inspector > >> Borough of Red Bank > >> Red Bank, New Jersey > >> Email: [email protected] > >> Cell/Text: 732-904-6823 > > > > > >> -----Original Message----- > >> From: [email protected] > >> [mailto:[email protected]] On Behalf Of > >> Rod DiBona > >> Sent: Monday, March 24, 2014 4:59 PM > >> To: [email protected] > >> Subject: truss filled with insulation > > > > >> I have an apartment building where the architect took the area > >> increases for a full 13 system. They are utilizing a 16"open web > >> truss in between the floors. The mechanical is running hvac in the > truss. > >> The sections show the space filled with insulation with an > >> accompanying note that states that it will be. My question is how is > >> this "completely filled with non - combustible insulation?" They are > >> planning on blowing in the insulation around all the duct etc that is > >> in the space but it just seems really hard to believe that it will > >> indeed be completely filled. I remember a while back Roland tried to > >> get a 2" gap on the top and I think that was a battle. I am picturing > >> the duct blocking insulation from getting in plenty of spots. > >> Maybe not? Any thougts? > > >> Rod at Rapid > >> _______________________________________________ > >> Sprinklerforum mailing list > >> [email protected] > > >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink > >> l > >> er.org > > > >> _______________________________________________ > >> Sprinklerforum mailing list > >> [email protected] > > >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink > >> l > >> er.org > > > > > > -- > > Ron Greenman > > Instructor > > Fire Protection Engineering Technology Bates Technical College > > 1101 So. Yakima Ave. > > Tacoma, WA 98405 > > > [email protected] > > > http://www.bates.ctc.edu/fireprotection/ > > > 253.680.7346 > > 253.576.9700 (cell) > > > Member: > > ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC > > > They are happy men whose natures sort with their vocations. > > -Francis Bacon, essayist, philosopher, and statesman (1561-1626) > > > A problem well stated is a problem half solved. -Charles F. > > Kettering, inventor and engineer (1876-1958) > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > > er.org > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > > er.org > > > > CONFIDENTIAL AND PROPRIETARY: > > This email message is intended only for the use of the individual or > > entity to which it is addressed and may contain information that is > > privileged and confidential, nor is it, unless specifically stated, > > intended to be relied upon by any person or persons other than the > > individual or entity named above and no warranties or representations > > are made or intended to persons or entities not named above. If the > > reader is not the intended recipient, you are hereby notified that any > > dissemination, distribution or copying of this communication is > > strictly prohibited. If you have received this communication in > > error, please notify us immediately by telephone, return this message > > to the address above and delete all copies. Thank you. > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > > er.org > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > > er.org > > > > -- > Best regards, > Charles Thurston mailto:[email protected] > Systems Design Manager > NICET Certified > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) A problem well stated is a problem half solved. -Charles F. Kettering, inventor and engineer (1876-1958) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org