I think Jim is also asking about Standard Response, right Jim? Why not put a standard response high temp head in there?
> On Mar 25, 2014, at 7:40 PM, Rod DiBona <[email protected]> wrote: > > My question is why? Why would not use an intermediate? I just don't get it? > > Rod at Rapid > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Scott A > Futrell > Sent: Tuesday, March 25, 2014 6:26 PM > To: [email protected] > Subject: RE: Re: > > I frequently see sprinklers rated at 155°F in utility closets with furnaces > that operate and cause a great deal of damage. > > > > Scott > > > > (763) 425-1001 Office > > (612) 759-5556 Cell > > > > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Forest > Wilson > Sent: Tuesday, March 25, 2014 1:40 PM > To: [email protected] > Subject: Re: > > > > I placed 155 in my home utility closet > > > > > >> On 3/25/2014 2:23 PM, [email protected]<mailto:[email protected]> >> wrote: >> >> We use intermediate for everything unless specifically forbiden. Have to >> watch out cuz some heads not available in intermediate. > >> > >> ----- Original Message ----- > >> From: Jim Adams [mailto:[email protected]] > >> Sent: Tuesday, March 25, 2014 01:11 PM > >> To: >> [email protected]<mailto:[email protected]> >> >> <[email protected]<mailto:[email protected]>> > >> Subject: > >> > >> > >> Ifyou have a closet solely with a washer/dryer should you put a standard >> temp orintermediate temp head in it ? FCU and hot water heater rooms are >> veryclear to use intermediate temp heads.. > >> _______________________________________________ > >> Sprinklerforum mailing list > >> [email protected]<mailto:[email protected]> > >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > >> > >> > >> _______________________________________________ > >> Sprinklerforum mailing list > >> [email protected]<mailto:[email protected]> > >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > > > > > -- > > Forest Wilson > > Project Manager > > > > 1855 Bellbrook Ave Ste C > > Xenia OH 45385 > > Ph: 937-736-0425 > > > > ///WHO IS JOHN GALT?/// > > > > ******This email and any files transmitted with it are confidential and > intended solely for the use of the individual or entity to whom they are > addressed. If you have received this email in error please notify the system > manager. This message contains confidential information and is intended only > for the individual named. If you are not the named addressee you should not > disseminate, distribute or copy this e-mail. Please notify the sender > immediately by e-mail if you have received this e-mail by mistake and delete > this e-mail from your system. If you are not the intended recipient you are > notified that disclosing, copying, distributing or taking any action in > reliance on the contents of this information is strictly prohibited.*** > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected]<mailto:[email protected]> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org