Tony, Sometimes people (especially older people) turn the heat up and it does get above 100 in the closet.
Sometimes furnaces don't operate properly and the high limit switch on most furnaces is >100, even greater than 130, I've seen them as high as 175 in furnaces in apartments that serve the corridor or common areas. I haven't seen an intermediate residential sprinkler operate in a furnace closet when it shouldn't have. I have seen ordinary temperature rated residential sprinklers operate in furnace closets when they shouldn't have. Scott -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Tony Palmero Sent: Tuesday, March 25, 2014 8:51 PM To: [email protected] Subject: Re: RE: Re: Yo forum, So we put in standard temp sprinklers in utility rooms all the time. From what my girlfriend says, we can put em in as long as the temp at the ceiling doesn't go over something like 100 degrees. Now I don't know about you, but I don't let it get above 100 in my house and the dryer is always vented to the outside. She'd kill me if I let the dryer heat (and fuzz) stay in the house. With that said, I can see where a guy would wanna use a 200-212 sprinkler to be safe...... but i understand they cost just a touch more. I also heard someplace that qwik response costs more than standard response. If that's true then things start to come real clear to me..... See ya, Tony P _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org