Tony,

Sometimes people (especially older people) turn the heat up and it does get 
above 100 in the closet.

Sometimes furnaces don't operate properly and the high limit switch on most 
furnaces is >100, even greater than 130, I've seen them as high as 175 in 
furnaces in apartments that serve the corridor or common areas.

I haven't seen an intermediate residential sprinkler operate in a furnace 
closet when it shouldn't have.  I have seen ordinary temperature rated 
residential sprinklers operate in furnace closets when they shouldn't have.

Scott 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Tony 
Palmero
Sent: Tuesday, March 25, 2014 8:51 PM
To: [email protected]
Subject: Re: RE: Re:

Yo forum,

So we put in standard temp sprinklers in utility rooms all the time.  From what 
my girlfriend says, we can put em in as long as the temp at the ceiling doesn't 
go over something like 100 degrees.  Now I don't know about you, but I don't 
let it get above 100 in my house and the dryer is always vented to the outside. 
 She'd kill me if I let the dryer heat (and fuzz) stay in the house.

With that said, I can see where a guy would wanna use a 200-212 sprinkler to be 
safe......  but i understand they cost just a touch more.  I also heard 
someplace that qwik response costs more than standard response.  If that's true 
then things start to come real clear to me.....

See ya,

Tony P