Let me clarify, It is stairs on the outside of a 2 story mezzanine that was supposed to be enclosed but the GC decided to get rid of the enclosure. There is currently full sprinkler protection at the roof deck ,each mezzanine level and a head installed under the lowest landing. The AHJ was walking through and asked if we needed a head at every landing and it got me wondering.
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Jeremy Frazier Sent: Wednesday, April 16, 2014 12:21 PM To: [email protected] Subject: RE: Stairs question If it is an open stairwell, usually you would put a water curtain around it & put sprinkler heads under the main landings. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Martinez, Dewayne Sent: Wednesday, April 16, 2014 12:32 PM To: [email protected] Subject: Stairs question For a non-combustible stairwell we typically put a head at the top of the stairwell and below the lowest landing for NFPA 13. What happens if the walls are removed from the scenario and we now have a exposed stair tower? We still ok with only two levels of sprinkler protection or must there now be sprinklers below every landing? Thanks, Dewayne _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler .org ______________________________________________________________________ This email has been scanned by the Symantec Email Security.cloud service. For more information please visit http://www.symanteccloud.com ______________________________________________________________________ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler .org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org