If it's on the outside, you probably wouldn't need any sprinkler heads. 2007
8.15.3.2.4.  Without seeing it, I think you would need one underneath each
main landing like you have, but to be honest, it does seem like a bit of a
grey area.  Potentially, if someone wanted to, they could make you protect
the stairs and the intermediate landings and you really wouldn't have any
code to fight it.  Because in combustible stairs you need to install
sprinklers beneath everything (establishes that there are situations where
the entire stair needs to be protected and that it isn't an unreasonable
position to require it).  The NFPA gives you an exemption for
non-combustible stairs in a shaft (sprinkler top and bottom).  If you take
away that exemption, pretty much your back to the obstruction rules.
Anything over 4'-0" needs sprinkers.  

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Martinez, Dewayne
Sent: Wednesday, April 16, 2014 2:21 PM
To: [email protected]
Subject: RE: Stairs question

Let me clarify, It is stairs on the outside of a 2 story mezzanine  that was
supposed to be enclosed but the GC decided to get rid of the enclosure.
There is currently full sprinkler protection at the roof deck ,each
mezzanine level and a head installed under the lowest landing.  The AHJ was
walking through and asked if we needed a head at
every landing and it got me wondering.   

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jeremy
Frazier
Sent: Wednesday, April 16, 2014 12:21 PM
To: [email protected]
Subject: RE: Stairs question

If it is an open stairwell, usually you would put a water curtain around it
& put sprinkler heads under the main landings.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Martinez, Dewayne
Sent: Wednesday, April 16, 2014 12:32 PM
To: [email protected]
Subject: Stairs question

For a non-combustible stairwell we typically put a head at the top of the
stairwell and below the lowest landing  for NFPA 13.

What happens if the walls are removed from the scenario and we now have a
exposed stair tower? We still ok with only two levels 

of sprinkler protection or must there now be sprinklers below every landing?

Thanks,

Dewayne 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to