This is the seats failing after a couple years with monthly testing while 
flowing through monitors.  They valves are above ground control valves for each 
monitor.  I suspect they are not opening the valve all the way so the 
velocities are unknown as I really don't know how far they are opening and the 
flow rate. 

Chris Cahill, PE*
Associate Fire Protection Engineer 
Burns & McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Spencer 
Allen
Sent: Wednesday, April 16, 2014 3:26 PM
To: [email protected]
Subject: RE: Valve Velocities

I have witnessed a lot of issues with the B/Fly Vv (Throttling Vv) on the pump 
test line.  If the Gate Valve (Isolating Vv) is opened very quickly the sudden 
impact of water against the B/Fly can break it. 

Previously we changed our pump flow test procedure to reduce the impact, by
either:

Open the gate valve very slowly to reduce the impact, Or Fully open the B/Fly 
valve before opening the gate valve, then throttle the flow down using the 
B/Fly valve.

We never received any definitive response from the valve suppliers.

Spencer Allen
Fire Engineering Solutions


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Art Tiroly
Sent: 16 April 2014 21:17
To: [email protected]
Subject: RE: Valve Velocities

I could see a lot of stress on the valve when it is nearly closed restricting 
the flow but not when it is fully open.

Art Tiroly
ATCO Fire Protection

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Cahill, 
Christopher
Sent: Wednesday, April 16, 2014 10:12 AM
To: [email protected]
Subject: Valve Velocities

Does anyone know if Listed control valves are tested at certain velocities and 
what that velocity is?  I mean the water flowing through them not throwing them 
in the air.  Theory is some butterfly valves failed due to too high velocity.  
I don't know right now what said velocity is.  While I figure that out I looked 
at the cut sheet and don't see a velocity limit in there.  I know for example 
double checks are tested at certain velocities and that information is right on 
the cut sheets.  In the test standard for valves is there a test requiring a 
minimum velocity test for a duration?

Chris Cahill, PE*
Associate Fire Protection Engineer
Burns & McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]<mailto:[email protected]>
www.burnsmcd.com<http://www.burnsmcd.com/>
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to