In 2007 it also had to be a single story to omit the FDC. Would it be required 
in a single story 1500 sqft footprint house with a basement?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)

> On May 23, 2014, at 11:07 AM, Roland Huggins <[email protected]> 
> wrote:
> 
> it isn’t the type of structure but the applied standard that dictates the 
> requirements for an FDC.  Note that 13R has an exception for small buildings 
> less than 2,000 sf.
> 
> Roland
> 
> 
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org
> 
> 
> 
> 
> 
>> On May 22, 2014, at 9:54 AM, [email protected] wrote:
>> 
>> 
>> Hello
>> 
>> this has to do with when egress windows are not provided in 1-2 family 
>> dwellings, and the sprinkler has to be designed per 13R as per IBC
>> is there an exception or industry std on whether to provide a local flow 
>> alarm and fire dept connection
>> 13 R says they are required 
>> does a private home need a fdc and a bell
>> 
>> certainly a 13r system will be safer than 13d in that more heads are 
>> calculated
>> 
>> 
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to