yes , I see the exception limited to 2000 sf or not more than 1 sty
we have a lot of jobs 2sty  and cellar.  townhouse jobs with an interior 
bedroom that uses a skylight to satisfy light and vent requirements.  however 
its not an egress window 
so then the design is by 13 or 13r
I was just trying to get a pulse on what other people are doing.  the building 
has not given anything in writing 

if there is a house fire the fire dept doesn't know which house is 13d or 13r , 
and in some properties the fdc may not be obviously found

 
 
 
 
-----Original Message-----
From: Roland Huggins <[email protected]>
To: sprinklerforum <[email protected]>
Sent: Fri, May 23, 2014 11:07 am
Subject: Re: 13R and 1 and 2 family dwellings


it isn’t the type of structure but the applied standard that dictates the 
requirements for an FDC.  Note that 13R has an exception for small buildings 
less than 2,000 sf.

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On May 22, 2014, at 9:54 AM, [email protected] wrote:

> 
> Hello
> 
> this has to do with when egress windows are not provided in 1-2 family 
dwellings, and the sprinkler has to be designed per 13R as per IBC
> is there an exception or industry std on whether to provide a local flow 
> alarm 
and fire dept connection
> 13 R says they are required 
> does a private home need a fdc and a bell
> 
> certainly a 13r system will be safer than 13d in that more heads are 
calculated
> 
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to