The only time I've mixed heads is when I have to protect a soffit, or some other type of hanging obstruction (i.e. ceiling cloud). I'll put SSP-QRs in the soffit and still have EC-QR's protecting the high ceiling if I cant space accordingly. The only other situation I've done this is when providing a water curtain.
Jerry Van Kolken Millennium Fire Protection (760) 722-2722 -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Sean Lockyer Sent: Wednesday, May 28, 2014 8:19 AM To: [email protected] Subject: Mixing EC-QR and SC-QR sprinklers in the same area Can Extended Coverage Quick Response Sprinklers and Standard Coverage Quick Response Sprinklers be mixed in the same compartment ? Even though QR and SR cannot be mixed within the same compartment (I.E.-Room) there is no rule precluding the mixing of EC-QR and SC-QR heads as far as I know. Does anyone here have any experience in this area ? Sean Lockyer Project Designer 4617 Parkbreeze Court Cell 386-279-1197 Orlando, Florida 32808 [email protected] Phone: 407-816-9101 www.AITLifeSafety.com Fax: 407-816-9104 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org